Heatmaker detonating on start up
Pelham
Member Posts: 3
in Gas Heating
My friend has a HeatMaker HW series that occasional will detonate on start up. What may be causing this? Could it be cross contamination?
It could be depending on how
it is vented. Some of them got there air for combustion from within the room others used a separate venting process for products of combustion and air for combustion, then still others used a concentric venting process which would be susceptible to cross contamination. Remove the connection and using a combustion analyzer the CO2 for air coming back into the unit should not read above 1% if it does the vent integrity has let go.
Has the unit been serviced? If not the chamber needs taken apart and cleaned, make sure the burner is inspected to make sure it is not damaged. Then do a combustion analysis on the unit.0 -
It is a two pipe with concentric termination, 3" internal exhaust and 5" air intake pipe in a pipe configuration. The problem is sporadic, sometimes not having a problem for months and other times multiple times in a day.0 -
Is it on natural gas or
LP? I would still take it apart and clean it just to be sure and do a combustion test.0 -
Yes, LP....that is what I'll do after I get a gasket kit for the kettle.0 -
It could also be because of the
LP with very low out door temperatures LP can sometimes delay on ignition.
.0 -
Seen it
Check the burner. If it starts like a shotgun there is a opening in the burner letting out too much gas. The two I've seen the seam weld opened up. You'll see it when you clean it..There was an error rendering this rich post.