friction loss
smklin
I am wondering how much friction loss i have i my heating system.
710' of 2'' pipe
2 2" 45 degree elbows
21 2" 90 degree elbows
and then i have 3 2" close return bends where the water makes a 180 degree turn
710' of 2'' pipe
what
kind of pipe? Also what flows rates do you want to look at? Just a guess will help.0 -
50 GPM
I HAVE 50< GPM
BLACK PIPE SCH 400 -
Resistance
At 50 gpm I came up with 4.66 ft of head/100 ft for 2" pipe.
After converting the fitting footage to ft of pipe the total equivalent feet came out to 919 ft including the 710 feet of pipe.
919 ft @ 4.66/100 ft =42.8' of head. the fitting chart I had showed 8.5 equivalent feet for a 2" screwed 90. This seems high to me.
What do you guys show for a 2" screwed 90?0 -
Ell
B&G lists 5 equivalent feet for a 2" screwed 90º ell .There was an error rendering this rich post.
pump
what pump will work on that0 -
Pump Curve
Go on Taco's web site and use their pump sizing tool.
I question using 2" for 50 gpm on a hydronic line. Your velocity maybe too high.Bob Boan
pipe velocity
At 50 gpm you are getting about 5 ft/s. Might be too fast? If you reduce your velocity your head loss will go down too.0 -
How much flow do you actually need?
Reducing flow and increasing ∆T will result pretty big wins both for first cost and electrical usage.
50 GPM = 42.4 feet (say 20ºF ∆T)
40 GPM = 27.9 feet at 25ºF ∆T
30 GPM = 16.3 feet at 30ºF ∆T0 -
< 50 GPM
I need 50 gpm. IF I COULD GET 60 I PROBABLY WOULD TAKE IT.0 -
in order of preference:
Reduce the GPM requirement (where did that come from, BTW)? Increase the ∆T, possibly with hydraulic separation and additional pump(s) downstream.
Replace as much of the run as practical with larger diameter pipe. Still better to isolate and branch where practical.
Install a big pump, eat the electric costs -- and be prepared for erosion corrosion.0
- 87.8K THE MAIN WALL
- 129 Chimneys & Flues
- 123 Geothermal
- 79 Pipe Deterioration
- 396 Solar
