Hate these things
M Lane
M Lane Member Posts: 123
Is this a White -Rogers? Does anyone know the wiring scheme, it is in an apartment with shared 24V. Client thinks this unit is under control from another unit, I'm 99% sure thats not the case. The thing is running open wild on its own.
  • icesailor
    icesailor Member Posts: 7,260
    edited January 2014
    You're welcome.
    You're welcome.
    How about posting some more information on what it is and what it is doing?
    It does look like some sort of a zone valve but I've never seen one like it. Judging by the smushed fin tube in the background and the valve handle, it must be a zone valve. More information would be helpful.
    Alan (California Radiant) Forbes Member Posts: 4,727
    edited January 2014
    White-Rogers
    I can't tell if it's a W-R or not, but I have a copy of the installation instructions and wiring diagram of the Type 1311 zone valve.  If you want a copy, send me your email address.
    Edit: It turns out to be available online here:
    http://www.emersonclimate.com/en-us/Products/Valves/Documents/0037-5421.pdf
  • Ironman
    Ironman Member Posts: 7,903
    Follow the terminals
    Two of them go to the motor. Two others to the end switch, and one is a blank terminal for splicing.
    Bob Boan
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,591
    Flair
    That is a Flair zone valve
  • Hydronicz
    Hydronicz Member Posts: 12
    here is the diagram
    Scroll to the middle of the page amd you will see wire diagram from 2 wire and 3 wire valve. Yours looks as if the top two wires go to the motor and the bottom are your 24v through your switch or thermostat.
    http://m.inspectapedia.com/?url=http%3A%2F%2Finspectapedia.com%2Fheat%2FThermostat_Diagrams.php#2706
  • Flair
    Flair zone valves are power open, power closed so maybe that third terminal is needed for the alternate operation.
  • M Lane
    Thanks guys
    Never even heard of Flair zone valves, I just assumed it was a WR. The end switches are not in use for anything. There's a bank of transformers at the boiler for all the ZV's and Tstats, but the boiler itself just runs on setpoint with an outside air cutoff switch only. Tha's the part I can never understand with these type of zv's in apartments. Why didn't they just just split the 24V circuit through the stat and call it good?