Hate these things
M Lane
Member Posts: 123
Is this a White -Rogers? Does anyone know the wiring scheme, it is in an apartment with shared 24V. Client thinks this unit is under control from another unit, I'm 99% sure thats not the case. The thing is running open wild on its own.
0
Comments
-
You're welcome.
You're welcome.
How about posting some more information on what it is and what it is doing?
It does look like some sort of a zone valve but I've never seen one like it. Judging by the smushed fin tube in the background and the valve handle, it must be a zone valve. More information would be helpful.0 -
White-Rogers
I can't tell if it's a W-R or not, but I have a copy of the installation instructions and wiring diagram of the Type 1311 zone valve. If you want a copy, send me your email address.
Edit: It turns out to be available online here:
http://www.emersonclimate.com/en-us/Products/Valves/Documents/0037-5421.pdf8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Follow the terminals
Two of them go to the motor. Two others to the end switch, and one is a blank terminal for splicing.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Flair
That is a Flair zone valveTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
here is the diagram
Scroll to the middle of the page amd you will see wire diagram from 2 wire and 3 wire valve. Yours looks as if the top two wires go to the motor and the bottom are your 24v through your switch or thermostat.
http://m.inspectapedia.com/?url=http%3A%2F%2Finspectapedia.com%2Fheat%2FThermostat_Diagrams.php#27060 -
Flair
Flair zone valves are power open, power closed so maybe that third terminal is needed for the alternate operation.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Thanks guys
Never even heard of Flair zone valves, I just assumed it was a WR. The end switches are not in use for anything. There's a bank of transformers at the boiler for all the ZV's and Tstats, but the boiler itself just runs on setpoint with an outside air cutoff switch only. Tha's the part I can never understand with these type of zv's in apartments. Why didn't they just just split the 24V circuit through the stat and call it good?0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements