Honeywell v8944n1053

Steve_210
Steve_210 Member Posts: 646
Just been told by my supplier that this gas valve has been replaced with the V8944N1012 does anybody know?

Thanks in advance

Comments

  • Tim McElwain
    Tim McElwain Member Posts: 4,612
    They are identical

    in just about all ways:



    Both Natural Gas 1' pipe size, 300 CFH to 1000 CFH, 6 second opening time, 24 volts,



    Both have regulator set points .8" W.C. to 2 " W.C.



    The one difference is the V8944N-1053  has a factory setting of 1.2" W.C. the V8944N-1012 factory setting .8" W.C.
  • Steve_210
    Steve_210 Member Posts: 646
    Thanks Tim

    For this and all the knowledge you share with us all.

    I always check the settings After installing anyway.