Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Honeywell v8944n1053
Steve_210
Member Posts: 647
in Gas Heating
Just been told by my supplier that this gas valve has been replaced with the V8944N1012 does anybody know?
Thanks in advance
Thanks in advance
0
Comments
-
They are identical
in just about all ways:
Both Natural Gas 1' pipe size, 300 CFH to 1000 CFH, 6 second opening time, 24 volts,
Both have regulator set points .8" W.C. to 2 " W.C.
The one difference is the V8944N-1053 has a factory setting of 1.2" W.C. the V8944N-1012 factory setting .8" W.C.0 -
Thanks Tim
For this and all the knowledge you share with us all.
I always check the settings After installing anyway.0 -
doesnt??
Doesn't your supplier provides you the needed information??0 -
Does yours
Are you always 100% confident with their info.
have you ever felt the need to get a second opinion?0 -
Nah
No need for a second opinion, he always takes the word of the 19 year old kid behind the counter. And he can adjust a flame by eye
Rob0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements