Honeywell v8944n1053

Steve_210
Member Posts: 647
in Gas Heating
Just been told by my supplier that this gas valve has been replaced with the V8944N1012 does anybody know?
Thanks in advance
Thanks in advance
0
Comments
-
They are identical
in just about all ways:
Both Natural Gas 1' pipe size, 300 CFH to 1000 CFH, 6 second opening time, 24 volts,
Both have regulator set points .8" W.C. to 2 " W.C.
The one difference is the V8944N-1053 has a factory setting of 1.2" W.C. the V8944N-1012 factory setting .8" W.C.0 -
Thanks Tim
For this and all the knowledge you share with us all.
I always check the settings After installing anyway.0 -
doesnt??
Doesn't your supplier provides you the needed information??0 -
Does yours
Are you always 100% confident with their info.
have you ever felt the need to get a second opinion?0 -
Nah
No need for a second opinion, he always takes the word of the 19 year old kid behind the counter. And he can adjust a flame by eye
Rob0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements