wiring a tekmar 519 tstat to sr506
wrxz24
wrxz24 Member Posts: 301
The problem I am having is that according to the manual, I need 4 wires, 2 for power(C and R) to the 24v on the taco, and 2 (Rh and W) for the on/of, and I only have 18/3 wire coming out of the wall.
Is there a way to wire the tstat without having to run new wire?
Thanks in advance
  • JohnNY
    JohnNY Member Posts: 3,324
    i would imagine..
    ....you could put a jumper from the R terminal to to the Rh?
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • wrxz24
    I tried that
    And it got power to the unit but the circulator would not run on a heat call. The tstat showed a heat call but the circulator would not run.
  • JohnNY
    hmmm
    If the light shows the call for heat at that zone, then the relay has pulled in. There's something else wrong. It's not your thermostat wiring. Check for 120v across your pump terminals. If you don't have it, swap out the corresponding ice cube relay with another one in the 506. See if that brings power to your terminals.
    Classes
  • wrxz24
    The light on the relay
    Does not turn on. The thermostat says "heat on" but the relay light is not on. When i hook my 2 wire wirsbo tstat back up, all works on a heat call.. If i jump wire from the 24 v to the T on the relay, the circulator kicks on.
  • JohnNY
    edited December 2013
    Interesting.
    In that case, you're right, there's an issue with the thermostat.
    I'm looking at the manual, like you are I'm assuming, and every diagram aside from the switching relay installation uses a jumper to power R -Rh.
    http://tekmarcontrols.com/images/_literature/519_dl_01.pdf
    No idea why yours isn't working. It looks like it should. I wonder if there's not an internal error in your 519.
    Classes
  • Zman
    Zman Member Posts: 7,611
    Commons
    That detail should work for you. The drawing on the bottom of page 9 of 16.
    Are you tying the commons back together in the mechanical?
    Instead of going too 7 and 2 on the 003, go to R and W.
    Hope that makes sense, The t-stat  control and the sr506 relay both need a common to work correctly.
    Carl
    Albert Einstein
  • wrxz24
    I got it to work
    Thanks fellas