Outdoor Sensor
Alan (California Radiant) Forbes
Member Posts: 4,570
Can I use a Munchkin outdoor sensor to replace a Viessmann outdoor sensor? Are they both 10K?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
10k
Not sure some use 12k. If you download the manuals for both, the info is probably there. I've got it on my laptop, but it's down at the moment.
As I'm sure you know the 10k is at 77*, so if you could check it at that temp. Most Tekmar sensors are 10k.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Munchkin Sensor
Just checked the Munchkin manual. The outdoor sensor is 12k and the indirect sensor is 10k.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
And just for the record
there a number of different 10k curves. Type 3 is probably the most common (most newer DDC systems) but there is a fair amount of Type 2 in use along with a few oddballs (especially on older systems.) http://www.veris.com/docs/support/faq/RTD-Thermistor_Z202030-0N.pdf
Honeywell MCBA (used in a LOT of mod/con boilers) uses 12k. I have yet to locate a full table for those, but Dale has a spreadsheet that generates them from Steinhart–Hart parameters.0 -
sensors are not always interchangable
even if they are the same resistance spec. I've tried this with a number of the Euro style solar controllers and some of the Euro boiler controls that all use PT1000 sensors.
There are also postiive and negative coefficient sensors PTC and NTC, resistance changes on temperature rise, or temperature fall. So unless you know the spec of the thermistor it may or may not work, or work properly.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It's never
straightforward is it? Especially with electronics. I guess it is what makes our job interesting, although it would be nice to have a "fits-all" sensor.
Thanks for your help, guys.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
This discussion has been closed.
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 117 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements