Will one of the wall unit condensing boilers work with cast iron radiators?
  • kcopp
    kcopp Member Posts: 4,630
    You betcha...
    If it is piped to specs. Furthermore it is a match made in heaven.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Radiators and new boiler
    It's a perfect combination of high mass radiators, and a modern condensing boiler. However, the cheaper look-a likes from the big box store may only be water-heaters, which will not work as boilers.--NBC
  • hairball
    Thanks
    Who makes the better condensing boilers?
  • hairball
    one more thing for now
    Some of the boilers I am looking at rated by input. How will I now what the output is. Right now I have a gas conversion burner that set up with 100,000 input would the condensing burner be about the same.
  • Zman
    Zman Member Posts: 7,611
    Heat loss
    The only way to correctly size a boiler is to do a heat loss calc.
    The output is the input derated by efficiency.
    A 100,000 BTU boiler that is 90% efficient would have an output  of 90,000 BTU at sea level.
    Lochinvar,Triangle tube and Viesmann  are some good choices.