I am installing a completely new 3 zone oil fired boiler in my house. converting from forced hot air to baseboard and radiant heat. Both on the same burner.
I have noticed there is a return loop from the supply line going directly into the return line with closely spaced T's.
My questions are:
----Do i put this return loop right as the supply line leaves the boiler? or do i run the supply line to the first two baseboard zones then before the 3rd radiant zone i T it off to the return line and to the 3rd zone.
----Should there be a 4th circulator pump in the main supply or return line for said loop?
----Should there be a Flow check in the loop, possibly between the closely spaced T's?
Any input would be greatly appreciated.
Thanks
Joe
My questions are:
Thanks
Joe
Drawing
It sounds like oil must be the only fuel available. Here is a calculator if you want to compare costs www.eia.gov/neic/experts/heatcalc.xls
A drawing of what you are proposing would be helpful.
If you are doing a radiant slab, you need to consider how you will prevent low return temps and boiler condensing.
I would suggest either an injection pump or 4 way mixing valve with outdoor reset and boiler protection. The Taco X block provides a good solution.
Albert Einstein0 -
simple design
It is a very simple design,
supply line to easy header for zone 1,2and 3
Zone 1 and 2 supply line connects to Circulator pumps zone 3 connect to mixing valve then to circulator pump. all 3 lines run their course and return to the return line back to the boiler. on the return line there is a line going to the mixing valve to supply cooler water to drop the temp to 120.
The radiant loop is a simple 100ft loop for under the kitchen floor attached between the floor joists in the basement.0 -
Drawing
It sounds like boiler condensing is not a concern and out door reset is optional.
If you post a drawing of what you are considering, we can provide you with more answers. There are so many ways people pipe boilers it is hard to follow your description.
Albert Einstein0 -
Sketch
Joe,
I am assuming you have a cast iron boiler?
You would not need any primary secondary if you did not have the radiant loop. Since the radiant loop can close off all flow to the boiler, I would do it primary secondary.
This is a rough (very) sketch of what I would suggest.
Albert Einstein0