3 zone boiler with 1 zone being radiant
pooteo
Member Posts: 19
I am installing a completely new 3 zone oil fired boiler in my house. converting from forced hot air to baseboard and radiant heat. Both on the same burner.
I have noticed there is a return loop from the supply line going directly into the return line with closely spaced T's.
My questions are:
----Do i put this return loop right as the supply line leaves the boiler? or do i run the supply line to the first two baseboard zones then before the 3rd radiant zone i T it off to the return line and to the 3rd zone.
----Should there be a 4th circulator pump in the main supply or return line for said loop?
----Should there be a Flow check in the loop, possibly between the closely spaced T's?
Any input would be greatly appreciated.
Thanks
Joe
I have noticed there is a return loop from the supply line going directly into the return line with closely spaced T's.
My questions are:
----Do i put this return loop right as the supply line leaves the boiler? or do i run the supply line to the first two baseboard zones then before the 3rd radiant zone i T it off to the return line and to the 3rd zone.
----Should there be a 4th circulator pump in the main supply or return line for said loop?
----Should there be a Flow check in the loop, possibly between the closely spaced T's?
Any input would be greatly appreciated.
Thanks
Joe
0
Comments
-
Drawing
It sounds like oil must be the only fuel available. Here is a calculator if you want to compare costs www.eia.gov/neic/experts/heatcalc.xls
A drawing of what you are proposing would be helpful.
If you are doing a radiant slab, you need to consider how you will prevent low return temps and boiler condensing.
I would suggest either an injection pump or 4 way mixing valve with outdoor reset and boiler protection. The Taco X block provides a good solution.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
simple design
It is a very simple design,
supply line to easy header for zone 1,2and 3
Zone 1 and 2 supply line connects to Circulator pumps zone 3 connect to mixing valve then to circulator pump. all 3 lines run their course and return to the return line back to the boiler. on the return line there is a line going to the mixing valve to supply cooler water to drop the temp to 120.
The radiant loop is a simple 100ft loop for under the kitchen floor attached between the floor joists in the basement.0 -
Drawing
It sounds like boiler condensing is not a concern and out door reset is optional.
If you post a drawing of what you are considering, we can provide you with more answers. There are so many ways people pipe boilers it is hard to follow your description.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Sketch
Joe,
I am assuming you have a cast iron boiler?
You would not need any primary secondary if you did not have the radiant loop. Since the radiant loop can close off all flow to the boiler, I would do it primary secondary.
This is a rough (very) sketch of what I would suggest.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements