Rat's Nest
Member Posts: 4,642
We've come a long way, haven't we.
Well, at least
you can replace the relays and transformer in that box- not always true with newer ones.
What is it used for- zone valves?All Steamed Up, Inc.
Consulting0 -
That's exactly
what I was thinking, Steamhead! But I didn't want to sound like I was an old-timer...Br. Jamie, osb
Controller
Frank: Those relays control pumps in a 5-unit apartment building.
When I first saw this, I wanted to sell the owners a more modern pump controller, but after thinking about it, I don't believe it would be in their best interests since those relays and transformer are probably original equipment. The pumps are all original Grundfos as well.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Do the relays
also start and stop the burner?All Steamed Up, Inc.
Consulting0 -
Burner
Yes, those relays turn on the burner.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
