first drop header
Paul S_3
Paul S_3 Member Posts: 1,288
Believe it or not after seven years first drop header....critics welcome.....Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • JStar
    JStar Member Posts: 2,752
    Header
    Sweet!
    The only thing I have to say is that we avoid installing unions on the horizontal. The pipes will move around and make them leak. Otherwise, great looking job.
  • ChrisJ
    ChrisJ Member Posts: 16,734
    Beautiful
    Beautiful work, but I would get rid of that evil autofeeder.  Either get rid of it and go 100% manual or get rid of it and install a VXT.
  • Paul S_3
    thank you guys
    What is a vxt..
    347-692-4777
    ASMHVACNYC.COM
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    Auto feeder choices
    The vxt has a built in meter, but I would still keep any auto-feeder valved off, for at least a couple of months, so as to see if there is any leakage.
    Auto-feeds are really the work of the devil!--nbc
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,917
    Automatic water-feeders
    The only problem with water feeders is that, in spite of what the literature that comes with them tells you, very clearly, they make some people think they don't need to mind the water level anymore. But that's not really the fault of the water feeder, now is it? You might as well say that bad near-boiler piping is the fault of steam boilers, not the knuckleheads who can't read and follow an IOM. I guess if you really believe people are just that intrinsically stupid, then they really should avoid water feeders, steam boilers and sharp objects, but I'm a little more optimistic. I believe people can be educated, and that, armed with the right information, they can make good decisions, and I don't think hyperbole about safety devices being "the work of the devil" is conducive to that end.
  • ChrisJ
    Hap
    Depends, either way the only feeder I'd ever put on my system is a VXT.
    Yes, it should ONLY be an emergency device and really should never turn on as the user\operator of the boiler should be manually adding. Still, I feel the VXT is a better feeder and the meter is a must. The feeder with the meter, has a good sound to it.
    I still don't have an autofeeder and may never for the simple fact I can't bare to think about my boiler sitting there with fresh water in it for any length of time, emergency or not. But we all know I'm weird.
  • Alan Welch
    Alan Welch Member Posts: 270
    Relief valve
    Don't see one, hope it is there somewhere.
  • Paul S_3
    relief valve
    Those weren't finished pics....these are them
    347-692-4777
    ASMHVACNYC.COM
  • Paul S_3
    edited April 2013
    347-692-4777
    ASMHVACNYC.COM
  • Paul48
    Paul48 Member Posts: 4,469
    Paul
    What's going on with the returns, and shouldn't they be connected below the water line?
  • Paul S_3
    returns
    they are below the waterline it just looks that way in the pictures
    347-692-4777
    ASMHVACNYC.COM
  • Hap_Hazzard
    I can't bear to think about all the water spewing out of my boiler and flashing to steam
    But I still have a relief valve on my boiler.
