Converting Crown Boiler
martin
martin Member Posts: 144
I'm going to convert a Crown CT3 boiler in a building I own. Two wholesalers have quoted me a Wayne P265FBB with conversion kit. Since not alot of oil is used in my area I have no experience in conversions.I'd like opinions on this burner and others.
    Steamhead Member Posts: 17,952
    Not a good choice
    the Freeport CT boilers come with Beckett AFG or Riello burners, which can develop the static air pressure needed to fire the boiler. That Wayne burner can't do this as far as I know. I'd use a Carlin EZ-Gas or Riello gas burner.
    All Steamed Up, Inc.
    Towson, MD, USA
    Oil & Gas Burner Service
    Consulting
  • martin
    riello burner
    Would you happen to have a model on the riello. Would it be the gulliver series ,having trouble with the riello site trying to find wholesalers.
    Towson, MD, USA
    Consulting