Job pics!
adambuild
Member Posts: 414
Hi Wallies,
Just before and after pics of a dead Glowcore and leaking Delta indirect that we replaced with a TT 110 LP and a Smart40. They're in a vacation home so we also put in a new Honeywell WiFi thermostat for remote control and monitoring of temperature. We also had a relay installed on the alarm system that automatically activates the indirect when the alarm is disarmed and shuts it down when the alarm is armed. Please forgive the old Spirovent. The owner didn't want to pay for a new one!? Whatever.
Adam
Adam
I couldn't get the second picture to enlarge.0 -
Hmm... It just opened for me...0 -
Same Here. Hey Dan.
Hopefully,
Dan will see this and get the tech guys to correct it. Some other recent post with multiple pics have had the same problem.Bob Boan
Good to see
Im not alone, last thing to happen are relief valve drops! Typically when I wait til the end they seem like the biggest chore in the world.
Nice looking jobTom
Montpelier Vt0 -
Agreed! I also insulated the pipes after that pic. Cleaning up the boiler room is never fun, but the TT purring in the background makes it bearable!0 -
Nice work...
You are forgiven for the used spiro , but the 1156 and dirty copper bypass unforgivable and where is the backflow LOL, jk, I think I see the back flo
it looks really good, I am buying my first 2 Prestige units Monday, I have been a loyal GB installer for a long time, may be time to switch up, looks very nice, Im putting one in my home and one in a customers, If Im going to sell them Im I try to use them for a while, who knows maybe Ill never hang the Buderus back up at my house after I start using the TT's... I use smart tanks all the time, I bought over 30 last year, and they never let me down..
Anyway, looks like you do nice work and take pride in it, getting to be hard to find...0 -
When I click on the second picture it opens an enlarged picture of the first one.0 -
Right click...
then select open in new tab or new window.
That will work...
JLG"Hey, it looks good on you though..."0 -
Question Concerning Exp Tank Placement
On the Solo 110 the boiler pump is on the supply so in essence you are pumping through the exp tank or point of no pressure change. Have you experience any issues?There was an error rendering this rich post.
is not using primary/secondary
good practice for these boilers? what did u do about dead heading post purge when the zone valves close? triangle tube arn't pushed very hard by supply houses here, mostly munchkin,peerless,navein.0 -
Also Have to Turn Off
Freeze protection. Funny how the manual has bold black and white that pri/sec is recommended but everyone always preaches direct pipe. Minimum flow rate at high fire is ignored consistently as well.There was an error rendering this rich post.
yea i seen that
and it says if u want/need to deviate from the recomended install, u should call the manufacturer.0 -
primary/secondary or direct
They start out with primary/secondary since it makes proper circulator selection (and consequent minimum flow rate) simple. Four pages later, one finds:
System Piping - Through Boiler
In new or retrofit applications in which primary/secondary arrangement is not utilized, the PRESTIGE Solo allows this flexibility due to a lower boiler pressure drop, see Graphs 2 through 7 on pages 91 through 93.
Figure 11, page 22 illustrates a multiple zone valve system with a single system/boiler circulator. A by-pass loop with a pressure differential valve must be installed on the system piping.
Figure 12, page 22 illustrates a single zone utilizing the boiler circulator as the system circulator.
Both topologies have their uses.0 -
Wow, look at the access for the original venting through the concrete!
Can you spell "Change-Order?"0 -
My Question is Exp Tank Placement
Since in the PT110 the onboard circulator is on the supply pumping away from the hx would it not be the best to install the exp tank on the return at the boiler?There was an error rendering this rich post.
no place else, really
head loss in the HX is low enough that they tolerate quite a bit of layout variation.0 -
Just to address several of the comments: The job is only one baseboard zone and the indirect, the factory was consulted regarding no primary/secondary, no problem. The pic of the new install was taken before insulating the pipes, removing the old vent piping (there's a foot of snow on the roof) and installing the copper extensions on the T&P valves, also, no pressure or air issues given expansion tank location. There is a backflow preventer (bottom left)! For the record, this is the first time ever that I didn't do primary/secondary piping. I only did it because the homeowner didn't want to pay for it and the factory gave their blessing. If I hadn't "cut that corner" the homeowner would've preferred an atmospheric/cast iron boiler and conventional water heater. That would've pained me with the potential LP fuel consumption. Just my thoughts.0 -
Factory?
So did the factory ask what your pressure drop was thru the system or did they just say it was OK with a baseboard system?0 -
direct pumped/piped
The 110 requires 5 GPM at maximum fire. The HX has two feet of head at that flow rate. It will work pretty much anywhere you put it.0
- 85.7K THE MAIN WALL
- 49 Biomass
- 72 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 48 Industry Classes
- 15 Recall Announcements
