What happens if you have a pressuretrol with the " diff " setting higher than the main setting , and the diff is subtractive ?

Comments

  • Steamhead
    Steamhead Member Posts: 18,851
    Haven't tried this

    but I'd think it would shut off on pressure, and not turn back on when the pressure drops. 

    Co-Founder, All Steamed Up, Inc.

    Baltimore, MD, USA

  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    Gonna have to try it

    next time I go back to do a skim and purge on a system . My guess is it would cut back in at 0 psi , but that;s just a guess .............. 
  • Jamie Hall
    Jamie Hall Member Posts: 27,766
    Steamhead's right...

    I've found that out the hard way.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • SWEI
    SWEI Member Posts: 7,342
    making it into

    a kind of manual reset high limit control?
  • Jamie Hall
    Jamie Hall Member Posts: 27,766
    Yeah,

    but that wasn't the idea at the time... !
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England