Pressuretrol setting question ......
Ron Jr._3
Member Posts: 605
What happens if you have a pressuretrol with the " diff " setting higher than the main setting , and the diff is subtractive ?
0
Comments
-
Haven't tried this
but I'd think it would shut off on pressure, and not turn back on when the pressure drops.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Gonna have to try it
next time I go back to do a skim and purge on a system . My guess is it would cut back in at 0 psi , but that;s just a guess ..............0 -
Steamhead's right...
I've found that out the hard way.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
making it into
a kind of manual reset high limit control?0 -
Yeah,
but that wasn't the idea at the time... !Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements