Zone short cycles and t stat reads lower than setting
davidheat
davidheat Member Posts: 4
I have a Utica gas fired hot water boiler and one of my zones cycles very quickly and then shuts off. The t stat is set at 68 and it reads as 61 actual temperature in the room.
any thoughts as to what I can check to try and correct?
  • Zman
    Zman Member Posts: 7,611
    Alittle more info
    Do you have zone valves or circulators?
    Can you post a picture?
    Carl
    Albert Einstein
  • Paul48
    Paul48 Member Posts: 4,469
    Thermostat
    Eliminate the thermostat by jumping it out, at the thermostat.Beyond that we need the info. There's a couple other possibilities.
  • unclejohn
    unclejohn Member Posts: 1,833
    Check
    The heat anticipater setting on the tstat.
  • davidheat
    edited January 2013
    Pictures
    I have Taco circulating pumps on each zone with Taco flo-chek valves. I have changed the caps on the flo cheks and that doesn't seem to fix it. Thanks
    Pictures attached.
  • davidheat
    Checked t-stat
    I checked the t-stat and the settings were correct, I would appreciate any help I can get. Thanks.
  • John Mills_5
    John Mills_5 Member Posts: 952
    Stat?
    Mechanical or digital?
  • davidheat
    Stat reply
    Hi John it is a Honeywell T87 t stat.
  • RobG
    RobG Member Posts: 1,844
    Zone Pump
    Is the boiler firing up on a call from the t-stat? If so, is it shutting down on high limit? If so, it sounds like your zone pump is not operating or the zone is air bound.
    Rob