Loud Smith gas boiler with Powerflame burner
DeeDeeM
DeeDeeM Member Posts: 4
Last year I had a Smith 28A-10 gas boiler installed with a PowerFlame burner.  The noise this creates is similar to a jet engine.
It is extremely bothersome to residents in the 5 story building.  I was told to try installing a silencing plenum in the duct breech.  I am concerned about having this done, as it is costly.  I also don't know who could do this type of work in my area.  Any ideas on other sound reducing methods??
  • Tim McElwain
    Tim McElwain Member Posts: 4,660
    What is your
    location?
  • Jim Davis_3
    Jim Davis_3 Member Posts: 578
    noisy burner
    I have never known Power Flame burners to be that noisy but a cast iron boiler should absorb most of the noise.  It is possible the burner needs better adjusting.  See if the people that service it have any combustion readings that you can give us.
  • DeeDeeM
    REsponse to my initial posting
    The burner has been down fired from 2.4 M to 1.6 m BTU's.  I will have to get the combustion readings from my vendor.
    I am located in Jersey City, NJ
  • Henry
    Henry Member Posts: 998
    A pro
    We install many 28A series. You need a pro who can properly adjust the burner and vent baffle at the boiler.
  • JStar
    JStar Member Posts: 2,752
    Burner
    Sounds a lot like too much combustion air.
    I service JC if you'd like our assistance