Zone short cycles and t stat reads lower than setting
davidheat
Member Posts: 4
in Gas Heating
I have a Utica gas fired hot water boiler and one of my zones cycles very quickly and then shuts off. The t stat is set at 68 and it reads as 61 actual temperature in the room.
any thoughts as to what I can check to try and correct?
Alittle more info
Do you have zone valves or circulators?
Can you post a picture?
Albert Einstein0 -
Thermostat
Eliminate the thermostat by jumping it out, at the thermostat.Beyond that we need the info. There's a couple other possibilities.0 -
Check
The heat anticipater setting on the tstat.0 -
Pictures
I have Taco circulating pumps on each zone with Taco flo-chek valves. I have changed the caps on the flo cheks and that doesn't seem to fix it. Thanks
Pictures attached.0 -
Checked t-stat
I checked the t-stat and the settings were correct, I would appreciate any help I can get. Thanks.0 -
Stat?
Mechanical or digital?0 -
Stat reply
Hi John it is a Honeywell T87 t stat.0 -
Zone Pump
Is the boiler firing up on a call from the t-stat? If so, is it shutting down on high limit? If so, it sounds like your zone pump is not operating or the zone is air bound.
Rob0
- 116 Geothermal