Zone short cycles and t stat reads lower than setting
 
            
                
                    davidheat                
                
                    Member Posts: 4                
            
                        
                
                                    
                                  in Gas Heating             
            
                    I have a Utica gas fired hot water boiler and one of my zones cycles very quickly and then shuts off. The t stat is set at 68 and it reads as 61 actual temperature in the room. 
any thoughts as to what I can check to try and correct?
                any thoughts as to what I can check to try and correct?
0                
            Comments
- 
            Alittle more info
 Do you have zone valves or circulators?
 Can you post a picture?
 Carl"If you can't explain it simply, you don't understand it well enough"
 Albert Einstein0
- 
            Thermostat
 Eliminate the thermostat by jumping it out, at the thermostat.Beyond that we need the info. There's a couple other possibilities.0
- 
            Check
 The heat anticipater setting on the tstat.0
- 
            Pictures
 I have Taco circulating pumps on each zone with Taco flo-chek valves. I have changed the caps on the flo cheks and that doesn't seem to fix it. Thanks
 Pictures attached.0
- 
            Checked t-stat
 I checked the t-stat and the settings were correct, I would appreciate any help I can get. Thanks.0
- 
            Stat?
 Mechanical or digital?0
- 
            Stat reply
 Hi John it is a Honeywell T87 t stat.0
- 
            Zone Pump
 Is the boiler firing up on a call from the t-stat? If so, is it shutting down on high limit? If so, it sounds like your zone pump is not operating or the zone is air bound.
 Rob0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements