gpm
Paul S_3
Paul S_3 Member Posts: 1,295
hey everyone....i have a question i just did a heat loss in a home today calculation came to 49,995btuh.....i did a calc for pipe size and circulator....gpm=btuh divided by (td mutiply 500)....came up with 5gpm.....so i would have to use 1'' pipe and baseboard.....home is small is there something not right here???can i use 3/4'' here would it be that much of a problem??
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Paul48
    Paul48 Member Posts: 4,469
    edited January 2013
    FloPro University
    In the variable speed pumping section.....there's a section on pipe sizing.If you've never checked the site out before....you'll be up late tonight.
  • Dave H_2
    Dave H_2 Member Posts: 622
    The pipe size
    Is also going to be dependent upon the head loss, then size your circ on that. 3/4" will give you a much higher head loss than 1", but if that fits in the realm of the circ, rock on.
    Otherwise, 1" may be the answer
    Dave H
    Dave Holdorf
    Taco, Inc
  • Zman
    Zman Member Posts: 7,611
    edited January 2013
    Split it.
    You can run 2-3/4" lines. It is often practical to run a 1" line to the center of the house then split to  2-3/4" lines.
    The other problem with piping 50K btu all in series, is that the radiators at the end will be starved and under perform.
    Carl
    Albert Einstein
  • Paul S_3
    zman
    I'm fine with the element I'm running two 3/4" zones....will not go over 67ft of element for 3/4"
    347-692-4777
    ASMHVACNYC.COM
  • Paul48
    Circ
    Are you going to use a delta-t circ?
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,289
    Put every room's
    Baseboard on either a Trv or a Zone Valve. Run 3/4" supply and return piped in reverse return. It will be a little more linear feet of pipe, but still less costly and more comfortable than running 1" with inline baseboard.
    Only 2% of a heating season will all zones be calling for heat at the same time. Engineer for comfort rather than max demand.
    Harvey