gpm

Paul S_3
Paul S_3 Member Posts: 1,261
hey everyone....i have a question i just did a heat loss in a home today calculation came to 49,995btuh.....i did a calc for pipe size and circulator....gpm=btuh divided by (td mutiply 500)....came up with 5gpm.....so i would have to use 1'' pipe and baseboard.....home is small is there something not right here???can i use 3/4'' here would it be that much of a problem??
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Paul48
    Paul48 Member Posts: 4,469
    edited January 2013
    FloPro University

    In the variable speed pumping section.....there's a section on pipe sizing.If you've never checked the site out before....you'll be up late tonight.
  • Dave H_2
    Dave H_2 Member Posts: 567
    The pipe size

    Is also going to be dependent upon the head loss, then size your circ on that. 3/4" will give you a much higher head loss than 1", but if that fits in the realm of the circ, rock on.

    Otherwise, 1" may be the answer



    Dave H
    Dave H
  • Zman
    Zman Member Posts: 7,609
    edited January 2013
    Split it.

    You can run 2-3/4" lines. It is often practical to run a 1" line to the center of the house then split to  2-3/4" lines.

    The other problem with piping 50K btu all in series, is that the radiators at the end will be starved and under perform.

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Paul S_3
    Paul S_3 Member Posts: 1,261
    zman

    I'm fine with the element I'm running two 3/4" zones....will not go over 67ft of element for 3/4"
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Paul48
    Paul48 Member Posts: 4,469
    Circ

    Are you going to use a delta-t circ?
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261
    Put every room's

    Baseboard on either a Trv or a Zone Valve. Run 3/4" supply and return piped in reverse return. It will be a little more linear feet of pipe, but still less costly and more comfortable than running 1" with inline baseboard.



    Only 2% of a heating season will all zones be calling for heat at the same time. Engineer for comfort rather than max demand.



    Harvey