gpm
Paul S_3
Member Posts: 1,288
hey everyone....i have a question i just did a heat loss in a home today calculation came to 49,995btuh.....i did a calc for pipe size and circulator....gpm=btuh divided by (td mutiply 500)....came up with 5gpm.....so i would have to use 1'' pipe and baseboard.....home is small is there something not right here???can i use 3/4'' here would it be that much of a problem??
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
347-692-4777
ASMHVACNYC.COM
FloPro University
In the variable speed pumping section.....there's a section on pipe sizing.If you've never checked the site out before....you'll be up late tonight.0 -
The pipe size
Is also going to be dependent upon the head loss, then size your circ on that. 3/4" will give you a much higher head loss than 1", but if that fits in the realm of the circ, rock on.
Otherwise, 1" may be the answer
Dave HDave Holdorf
Taco, Inc
Split it.
You can run 2-3/4" lines. It is often practical to run a 1" line to the center of the house then split to 2-3/4" lines.
The other problem with piping 50K btu all in series, is that the radiators at the end will be starved and under perform.
Albert Einstein0 -
zman
I'm fine with the element I'm running two 3/4" zones....will not go over 67ft of element for 3/4"ASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Circ
Are you going to use a delta-t circ?0 -
Put every room's
Baseboard on either a Trv or a Zone Valve. Run 3/4" supply and return piped in reverse return. It will be a little more linear feet of pipe, but still less costly and more comfortable than running 1" with inline baseboard.
Only 2% of a heating season will all zones be calling for heat at the same time. Engineer for comfort rather than max demand.
Harvey0