Trimax / DHW question
adambuild
Member Posts: 420
I have a job with a TT 110 with Trimax control and a Smart 40 indirect. I'd like to install the optional sensor in the indirect and remove the aquastat but I have a challenge. The homeowner wants to remotely control the indirect with a pair of dry contacts. I used to just interrupt the aquastat for that purpose but suspect that interrupting the optional sensor will cause a lockout. I'd rather use the sensor because it gives more accurate control of the indirect temperature. Any ideas?
Thanks, Adam
Thanks, Adam
remotely control what?
What is the homeowner trying to accomplish?0 -
Its either or...
not both. Does he want to put it on a timer? If he is concerned about stand by loos there isn't much... be sides letting the water drop to lower temps in a tank for long periods of time a lot invites legionella0 -
This will work
Disable the domestic hot water priority on the controller and then break the hot leg of the dhw circ. through your dry contacts.0 -
It's a vacation house. He can already turn the heat up and down with a new Honeywell Wifi stat we put in and he wants to be able to remotely control the indirect as well. He lends the house out a lot and wants to be able to shut down the indirect if no one will be using the house for a few weeks.
Thanks, Adam0 -
Not the best...
Disabling the DHW circ will not make the call go away. The boiler will still try to heat the tank.
I think you would be better off with your original plan without the sensor.
Tekmar does a nice job with this. You can put the entire system including t-stats in an away mode.
Given the low heat loss in the smart tank, I would be inclined to leave it on. Be sure to insulate the pipes and provide heat traps on the lines to prevent migration.
Albert Einstein0 -
Ok try this
Find out from TT what resister you need to make the boiler think the tank is 140*F and switch from resister to sensor with a 4 pole relay.0 -
resistor
A 3.3kΩ resistor and a set of SPDT contacts will do the trick.0 -
Thank you Uncle John and SWEI, just what I was looking for!!! Thank you to the others as well for the valuable input!!!
Adam0