wall furnace
RJ_4
RJ_4 Member Posts: 484
A friend of mine wants to install a wall furnace in a remodeled garage, at this point it is 1 big open rm 400 sq. ft  Option 1, the easiest,   mount heater on the inside of the outside wall. (closest to gas line )  Option 2 build a small interior wall in rm and install a dual wall heater.  Asking for opinions. I worked in the commercial side of the trade and am not familiar with wall heaters
Thanks Rick
  • Tim McElwain
    Tim McElwain Member Posts: 4,657
    Is this a direct vent
    heater (concentric vent) or does it use Type BW vent (double wall oval shaped)?
  • RJ_4
    cozy
    It is a cozy wall heater, it uses double wall oval pipe,  25mbh
  • Tim McElwain
    Does it get its air for combustion
    from within the room and does it have a pilot? If so it has to be 18" off the floor off the garage also follow venting instructions as vent termination and vent location in relation to walls or parapets. They can only be installed in single story dwellings. It will need a header plate in accordance with section 10-27 of the National Fuel Gas Code NFPA 54/ANSI Z223.1. They are installed in the wall cavity between 2 x 4 construction.
  • RJ_4
    wall furnace
    I will check all these things
    Thanks Rick