Piping radiant heat mixing valve
Billjulian
Member Posts: 12
A Taco 5000
is pretty limited as to what you can do w/ it. With that setup a motorized mix valve w/ outdoor reset built... like a taco i valve would be best. http://www.taco-hvac.com/en/products/iSeries%20Mixing%20Valves/products.html?current_category=1880 -
Radiant mixing valve
Thanks what model would you recommend?0 -
How is the tubing installed
Is this a staple up application? Do you have the ability to measure the pipe temps accurately?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Upside down
Just to be sure... The "C" is pointed up right?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Ya the C is pointed up.0 -
Motorized Taco 3-way valve
What will a motorized valve do for me over a Taco 5000? I never installed one how does a motorized valve operate?0 -
motorized valve
can change the supply temp based on the outdoor temperature. This is called outdoor reset (ODR) and will improve both comfort and efficiency.0 -
Radiant Mixing
Thanks Swei
What is happening is...the return water (teed in from the cooler zone) seems to be a problem. I am thinking of re piping the cooler (cold) side of the Taco 5000 so it is horizontal because my other radiant zone works fine. The set up is: Cold to the left hot to the right and mixed facing upward.
I think the return water is struggling it may be a heat trap if you look at the pic because when I put my hand on the cooler return water right at the Taco 5000 it is very warm not much cooler than the hot side.0 -
what temp is the valve set for?
can't tell what your piping is doing. supply water (hot) should be on hot side, your mixed circuit return water should be cold side, and you should be pumping out of your mix outlet to the mix supply side.
if you are doing that you should never exceed the temp setting on the valve. you are getting near max temp so either you have it piped wrong or you have the setting at max.Rob Brown
in beautiful Rockport Maine.0
- 87K THE MAIN WALL
- 114 Chimneys & Flues
- 106 Geothermal
- 982 Plumbing
- 388 Solar
