Where should the expansion tank go and why?
ChrisJ
ChrisJ Member Posts: 17,070
I'm reading Dan's book "Pumping Away" and at this point one thing confuses me.  Where should the expansion tank go as a rule?
If the expansion tank goes on the supply as a rule, why?  WIll it work just as well on the return assuming the pump is on the return right after the expansion tank?
Being the book talks about the best place for the circulator being on the supply I have to assume the expansion tank also belongs on the supply, but I don't understand why.
Thanks,
Chris J
  • Zman
    Zman Member Posts: 7,611
    I think it is all in the book.
    The air scoop, which is often attached to the expansion tank. It will function better with hotter water and at lower pressure.
    The T&P on the boiler does not want the extra pressure.A high head circulator pumping into the boiler could set off the T&P. Picture a system pressure of 18# with a 13# circ head pressure. It would trip a 30# T&P.
    Albert Einstein
  • alotlikeearl
    alotlikeearl Member Posts: 68
    edited October 2012
    Check Out
    Here is info from Burnham's Heating Helper that may help.
    "Pumping Away"...but from what?
    The question still at hand is where to place the circulator in the system
    so it reaches its maximum effectiveness. This is where the term “pumping
    away” sometimes gets misconstrued. Many believe that the term
    “pumping away” means to pump away from the boiler and therefore
    they end up mounting the
    circulator directly off the top
    of the boiler on the supply
    pipe. While this may seem
    to be somewhat correct, in
    reality it is wrong. The real
    meaning of the term “pumping
    away” means pumping away
    from the system expansion
    or compression tank. The
    reason for this has to do
    with the functions that the
    circulator and expansion tank serve. The function of the circulator is
    to create a pressure differential and the function of the expansion tank
    is to regulate the system pressure as close to static fill as possible. If
    the tank encounters a drop in pressure it will try and fill that pressure
    void and if it encounters a pressure increase due to mechanical means
    or thermal expansion, it will try and absorb it. When a circulator is
    mounted on the boiler supply but is situated before the expansion tank,
    nearly all of the extra discharge pressure that the circulator is capable
    of developing will be absorbed by the expansion tank resulting in static
    fill pressure or less being exerted through the system piping. The water
    will still move through the system but there will be relatively low system
    return side pressures and more than likely, captive air and noise will be
    encountered in the farthest circuits of the system. When the circulator
    is mounted on the system supply directly after (as close as possible)
    the expansion tank you will now be exerting the extra pressure it is developing
    where it is needed most or to the system supply piping. Now it
    will more effectively move the water and keep high enough pressures
    in the remote portions of piping to prevent air from accumulating or
    coming out of solvency. The lesser pressure that pump is developing
    on its suction side will be in contact with the expansion tank. The action
    now will be that the expansion tank diaphragm will move into place to
    fill that pressure void causing an increase to static fill pressure at the
    suction side of the pump.
    The end result will be a well working, quiet and captive air free system
    with no consumer complaints or callbacks. In final review, the term
    “pumping away” means pumping away from the expansion or compression
    tank.
    sion
    tank.
    hot_rod Member Posts: 26,604
    check out this article
    from the Plumbing & Mechanical website. Siggy does a great job of explaining the concept with both cast iron boilers and hydro separators.
    www.pmmag.com/Articles/Column/BNP_GUID_9-5-2006_A_10000000000000657694