Where should the expansion tank go and why?
ChrisJ
Member Posts: 17,070
I'm reading Dan's book "Pumping Away" and at this point one thing confuses me. Where should the expansion tank go as a rule?
If the expansion tank goes on the supply as a rule, why? WIll it work just as well on the return assuming the pump is on the return right after the expansion tank?
Being the book talks about the best place for the circulator being on the supply I have to assume the expansion tank also belongs on the supply, but I don't understand why.
Thanks,
Chris J
Thanks,
Chris J
I think it is all in the book.
The air scoop, which is often attached to the expansion tank. It will function better with hotter water and at lower pressure.
The T&P on the boiler does not want the extra pressure.A high head circulator pumping into the boiler could set off the T&P. Picture a system pressure of 18# with a 13# circ head pressure. It would trip a 30# T&P."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Check Out
Here is info from Burnham's Heating Helper that may help.
"Pumping Away"...but from what?
The question still at hand is where to place the circulator in the system
so it reaches its maximum effectiveness. This is where the term “pumping
away” sometimes gets misconstrued. Many believe that the term
“pumping away” means to pump away from the boiler and therefore
they end up mounting the
circulator directly off the top
of the boiler on the supply
pipe. While this may seem
to be somewhat correct, in
reality it is wrong. The real
meaning of the term “pumping
away” means pumping away
from the system expansion
or compression tank. The
reason for this has to do
with the functions that the
circulator and expansion tank serve. The function of the circulator is
to create a pressure differential and the function of the expansion tank
is to regulate the system pressure as close to static fill as possible. If
the tank encounters a drop in pressure it will try and fill that pressure
void and if it encounters a pressure increase due to mechanical means
or thermal expansion, it will try and absorb it. When a circulator is
mounted on the boiler supply but is situated before the expansion tank,
nearly all of the extra discharge pressure that the circulator is capable
of developing will be absorbed by the expansion tank resulting in static
fill pressure or less being exerted through the system piping. The water
will still move through the system but there will be relatively low system
return side pressures and more than likely, captive air and noise will be
encountered in the farthest circuits of the system. When the circulator
is mounted on the system supply directly after (as close as possible)
the expansion tank you will now be exerting the extra pressure it is developing
where it is needed most or to the system supply piping. Now it
will more effectively move the water and keep high enough pressures
in the remote portions of piping to prevent air from accumulating or
coming out of solvency. The lesser pressure that pump is developing
on its suction side will be in contact with the expansion tank. The action
now will be that the expansion tank diaphragm will move into place to
fill that pressure void causing an increase to static fill pressure at the
suction side of the pump.
The end result will be a well working, quiet and captive air free system
with no consumer complaints or callbacks. In final review, the term
“pumping away” means pumping away from the expansion or compression
tank.sion
tank.0 -
check out this article
from the Plumbing & Mechanical website. Siggy does a great job of explaining the concept with both cast iron boilers and hydro separators.
www.pmmag.com/Articles/Column/BNP_GUID_9-5-2006_A_10000000000000657694Bob "hot rod" Rohr
Living the hydronic dream0