Radiant floor with domestic h20
I have a room with under floor radiant that will be connecting off of a domestic tank, i am going to use a 2 circuit manifold. Any decent piping diagrams would be helpful.
  • kcopp
    kcopp Member Posts: 4,610
    don't do it....
    plain and simple. You are contaminating your water supply and risk harming your heath.... Use a separate heating set up.
  • Vito200
    Vito200 Posts: 4
    This is a Vertex with seperate hydronic tappings
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,422
    They are not made for radiant heating
    they are made to go to an air handler with a round trip of less than 50 feet total. Radiant heat is a breeding ground for bacteria and should only be connected through a heat exchanger to this unit.
    cell # 413-841-6726
  • Zman
    Zman Member Posts: 7,611
    Closed?
    Unless the heater has a "closed" hydronic coil. Don't do it. Just because some manufactures are enabling people to put in unsafe systems, it is still the wrong way to do it.
    Albert Einstein
  • billtwocase
    billtwocase Member Posts: 2,384
    ditto
    Ditto.
  • Vito200
    Vito200 Posts: 4
    Radiant h20
    I am using a plate heat exchanger , any piping diagrams?
  • Zman
    Personal preference
    There are quite a few ways to do this. How much detail are you looking for? You need to pump from the hot water heater in the exchanger. My plan for the other side would be to use a variable speed pump controlled by a tekmar 356 with outdoor reset to in inject the water into the radiant loop from the exchanger. This way you can control the floor temps and avoid dragging down the hotwater temp using the boiler protection feature on the controller. You will of course need air eliminators,zone valves, pumps ect. to control the radiant side.
    Albert Einstein
  • duffy_4
    duffy_4 Member Posts: 79
    Taco x block
    Just used the taco x block on two separate installs here in the city ,4 units of a condo complex I found with open systems,worked beautifully simplified piping in a tight spot.still trying to convince other two owners to change theirs or at the least not used it as is.
  • kcopp
    I 2nd..
    the X-block. A sinple all in one design ... air seperation, HX, and control. They have nice diagrams. http://s3.pexsupply.com/manuals/1326240192388/70252_PROD_FILE.pdf
  • Vito200
    Vito200 Posts: 4
    Good Call looks like the best approach using the Taco x block
    Thanks
  • Sol Hydronics
    Sol Hydronics Member Posts: 41
    X block
    I have used the X block on a water heater to go to just a bath floor with outdoor reset and no t-stat and it works great