Remote CompressionTank
ChasMan
ChasMan Member Posts: 474
I'm short on space for a larger compression tank. By my calculation I need 14 gallons (have 7). I can;t add another one so I was considering remoting them to the water closet. So, I would have the backflow / feed valve combo and twin 7 gallon tanks about 20 feet from the boiler. I would put a ball valve at the boiler for servicing. Does anyone see any problems with that arangement?
  • Ironman
    Ironman Member Posts: 7,859
    No Problem...
    So long as they connect back to the system where the PONPC is upstream of the circ. and the interconnecting line is of sufficient size (you may want to use 3/4").
    Bob Boan
  • kcopp
    kcopp Member Posts: 4,630
    yes...
    I do it all the time.... ok maybe not 25' from the ponpc... but 5'...kpc
  • ChasMan
    Great.
    Ok, I will go ahead with this scheme. Thanks a lot.