Remote CompressionTank
Options
ChasMan
Member Posts: 474
I'm short on space for a larger compression tank. By my calculation I need 14 gallons (have 7). I can;t add another one so I was considering remoting them to the water closet. So, I would have the backflow / feed valve combo and twin 7 gallon tanks about 20 feet from the boiler. I would put a ball valve at the boiler for servicing. Does anyone see any problems with that arangement?
0
Comments
-
No Problem...
So long as they connect back to the system where the PONPC is upstream of the circ. and the interconnecting line is of sufficient size (you may want to use 3/4").Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
yes...
I do it all the time.... ok maybe not 25' from the ponpc... but 5'...kpc0 -
Great.
Ok, I will go ahead with this scheme. Thanks a lot.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements