Remote CompressionTank

ChasMan
Member Posts: 472
I'm short on space for a larger compression tank. By my calculation I need 14 gallons (have 7). I can;t add another one so I was considering remoting them to the water closet. So, I would have the backflow / feed valve combo and twin 7 gallon tanks about 20 feet from the boiler. I would put a ball valve at the boiler for servicing. Does anyone see any problems with that arangement?
0
Comments
-
No Problem...
So long as they connect back to the system where the PONPC is upstream of the circ. and the interconnecting line is of sufficient size (you may want to use 3/4").Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
yes...
I do it all the time.... ok maybe not 25' from the ponpc... but 5'...kpc0 -
Great.
Ok, I will go ahead with this scheme. Thanks a lot.0