low water cutoff
zepfan
Member Posts: 444
can an existing steam boiler with float type low water cutoff be retrofitted with a probe type lwc and a seperate electric water feeder?
It Depends
We'll get back to you on that.
Please post pictures of what you have.All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
modifications
is there a good reason to make these changes?
i regard the auto/over feed as being responsible for many boiler rot-outs as a result of the lack of attention [on the owner's part] which is then permitted.--nbc0 -
Yes.
Yes, an existing steam boiler with float type low water cutoff can be retrofitted with a probe type LWCO and a separate electric water feeder. I just did this to mine.
Can any existing steam boiler be retrofitted with a probe type lwc and water feeder? Not necessarily. A water feeder can usually be added without changing the LWCO, and if a probe-type LWCO was available as an option on your boiler, you can probably install one on yours.Just another DIYer | King of Prussia, PA
Pay attention
if you do put an auto feeder on; as NBC says make sure there is a flow counter on it and that you pay attention to the dang thing.Br. Jamie, osb