can an existing steam boiler with float type low water cutoff be retrofitted with a probe type lwc and a seperate electric water feeder? 

Comments

  • Gordo
    Gordo Member Posts: 857
    It Depends

    We'll get back to you on that.



    Please post pictures of what you have.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • modifications

    is there a good reason to make these changes?

    i regard the auto/over feed as being responsible for many boiler rot-outs as a result of the lack of attention [on the owner's part] which is then permitted.--nbc
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    Yes.

    Yes, an existing steam boiler with float type low water cutoff can be retrofitted with a probe type LWCO and a separate electric water feeder. I just did this to mine.



    Can any existing steam boiler be retrofitted with a probe type lwc and water feeder? Not necessarily. A water feeder can usually be added without changing the LWCO, and if a probe-type LWCO was available as an option on your boiler, you can probably install one on yours.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • Jamie Hall
    Jamie Hall Member Posts: 24,842
    Pay attention

    if you do put an auto feeder on; as NBC says make sure there is a flow counter on it and that you pay attention to the dang thing. 