Has anyone had problems with Dunkirk Boilers?
BadQ90
Yes, everythig is within spec, combustion, gas, pressure..0 -
BadQ90
Thank you Andy,
Scott sent me an e-mail, I left him a phone msg today, he called me back. We've been playing phone tag today but have a plan to connect on Monday. I am grateful for his contact. Just came home and the heat was out. I'll be brief, no lights on the control board, cycle power, and away she goes.... maybe it just misses me when I'm gone....:)0 -
Maybe not so bad Q90
Final chapter:
Since my last post, I had a lengthily conversation with Scott Dam at ECR about the operational characteristics of the unit which was very enlightening. Scott is very knowledgeable and arranged a visit to my home by their Regional Sales Manager a person from their Technical Service department. Both of these gentlemen were professional, knowledgeable and I want to thank them for taking time out of their busy schedules to address my boiler issues. Also present was my heating contractor.
My boiler was manufactured in 2005 so the first thing I wanted to know, was are there any parts or configurations of parts in my boiler now which were suspect, out dated, in need of modification or replacement or are there any components which ECR had found to be suspect or marginal in function either due to design or manufacture supplier issues? After review and taking lots of pictures, the answer was no, all parts were OK. I had already had the burner upgrade (I’ll get to that in a moment) so there was nothing else from a component perspective in need of updating or which would have caused the random shutdowns.
With regard to the combustion mix, the spec calls for a max limit of 10% CO2, I rechecked it myself after the last visit from my heating person who said it was OK, and it turned out to be about 11.3%, guess he thought that was close enough. I adjusted the throttle screw down till the reading was 9.2, right center in the allowable range. This took about 6 turns of the throttle screw from where it was. It also reduced the burn rate from 200KBTUs to 175K BTUs as measured by the gas meter. There is no trail to figure how my 175K boiler got set to exactly 200K, so that still bothers me a bit, but it is correct now and will remain a mystery forever more.
So, with regard to the comment made that because of the burner upgrades “I now have a 200K boiler”, that is an incorrect statement. Scott at ECR said that the 175 and the 200 use the same burner part to make it easier on people who have to stock parts, but that alone does not change a 175K into a 200K boiler.
The throttle adjustment screw not only changes the mixture, but it also has a significant impact on the burn rate, enough to easily make my 175K burn at a 200K, and probably has enough range in it to go even higher, or lower I would suspect, all this while the flame “looks good”. My CO2 was over the high limit by only 1.3%, but this setting induced an increase in burn rate of over 25k BTUs! This probably means that even within the allowable specs for CO2, a range of 8.5% to 10% , a span of 1.5%, there is some variability as to what the burn rate will be, perhaps even around the same 25K worth of BTUs across the in-tolerance range. So, even with CO2 is set somewhere within the allowable range, your burn rate may be off.
From a procedural perspective, to properly tune this boiler one needs to ensure the CO2 is set in the allowable range to start with and then go to the meter and carefully calculate the gas flow, adjusting the throttle screw such that the gas usage is also correct for the boiler size, while maintaining a CO2 in range. It takes both CO2 and gas flow to tune the thing properly and it takes one or two iterations back and forth between the gas meter and the CO2 meter to get both the CO2 levels and the gas flow usage correct. You must measure both. While this may seem obvious to some of you reading this, it escaped the heating contractors who installed and worked on my unit.
My boiler was over fired, that is bad, but didn’t necessarily explain the intermittent shut downs. We then measured the gas pressure. The static pressure was 6.9 inches, but with the burner on it dropped to 2.5 inches which is below the 4 inch minimum pressure spec. This is very bad and could cause a flame failure which would manifest as a random, intermittent shutdown problem! How about that! Suspecting a bad gas regulator, I called the utility that came and changed my meter and pressure regulator. Now I have 7 inches static and 4.5 inches at the boiler, which is in spec for the boiler when the burner is on. However, I was unsatisfied with such a large unexplained pressure drop. With the help of the utility company person we measured the gas pressure on some piping near the boiler, but not on the feed to the boiler and it was about 6 inches, turning on other appliances such as the stove and gas dryer and it maintained 6 inches. Therefore, the piping to the boiler is too restrictive. Looking at the configuration feeding the boiler consisting of a 5 foot section of ½ inch pipe, with two ball valves, 1 “T” and about 4 elbows, we surmised that this stuff would be better if it was ¾ inch for less drops when the boiler is on.
What caused my shutdowns? The current theory the gentlemen from ECR are going with and for now one which I concur with is that the lower gas pressure may have caused the burner flame to fail. If the gas pressure off the street went down, like in the dead of winter and when everyone’s boiler on the block going full blast, (I’m at the end of the line) the pressure may have dropped low enough to cause a failure. Given that the burner only seemed to fail when it was very cold out, and quite often on a Saturday night or weakened (when people are home using heat?) this low pressure gas theory does fit the symptoms, the fact that my boiler was using an extra 25K BTU’s probably didn’t help the situation.
For now I am satisfied that the failure theories, troubleshooting discoveries and recommended fixes all seem to fit the symptoms which I have been experiencing. I hope my detailed explanation of this situation serves to help someone else who may be having similar problems.
However, I am deeply disappointed in some of the heating professionals who came to my home and have worked on this boiler with only a casual understanding its fundamental operating characteristics and obliviously not enough training to properly adjust the system and diagnose the issues. These new HF boilers are nothing like old cast iron ones, previous assumptions of what a good or bad flame looks like may not apply. By the time a flame looks questionable, the unit is probably very far out of spec and unforgiving of the condition. After adjustment, the change in my flame was barely noticeable! These systems are particular, finicky and demanding, they need to be set up perfectly for reliable operation and “perfect” is defined as the sum of a combination of measurements which converge on an optimum setting. It has cost me over a thousand dollars in service calls over the years and many hours of personal learning to find what turned out to be a very basic problem which should have been easily recognized by any heating professional. It is clear to me that they wanted to get in and out of my house as quickly as possible and really didn’t understand the sensitive set up points of unit.
There is also a discussion to be had about cleaning and flushing the unit, and if the unit is in condensing mode or not which tends to have a flushing effect on the oxides if it is, but I’ll leave that discussion to someone else.
In conclusion, I would apologize to the folks at ECR for some of the abuse I have dished out in this post about the unit, even though these posts are what it took to get enough attention and people here who knew what they are doing. Understand my frustration had reached the breaking point because I believed the heating professionals I was working with understood the unit. In the end their knowledge was only casual and insufficient to see the “big picture” or even the little details. The good folks at ECR came through with an onsite visitation from two very qualified people, Don DeCarr from Technical service and Robert Shea, the Regional Sales Manager (here in NY), both of these gentlemen went out of their way to come to my home, were very professional and knowledgeable as was Scott and I appreciate their time, effort and expertise. Thank you to EC for allocating the necessary resources to get my problems resolved.
I’m very optimistic that we have identified and corrected the root cause of the random shutdown issue, that there are no latent engineering or design problems with the unit and there will be no more problems.
Farewell and good heating to all,
On to Air-conditioning season! J0 -
Good News!!!!
Glad to hear you have solved your issues. Hopefully you can enjoy the rest of winter and look forward to spring. Keep us posted!0 -
Glad to Hear...
That it seams like you've gotten your problems solved. As I stated in my earlier posts, the folks at ECR are good people and usually go out of their way to help.
And as I also stated, and so many of us here know all too well, the problems are almost always installer/servicer related. Too many in this trade don't put the time, effort and $$$ into getting proper training, tools and equipment or staying abreast of the latest technology so they can do the job right. Then when they can't fix it, they tell the customer there's something inherently wrong with the appliance and the manufacturer should do something about it.
Hope you have many trouble free years of service from your boiler.Bob Boan
Unfortunately...
very few technicians have the equipment necessary to properly diagnose combustion equipment. Even sadder, those that do have the proper equipment either don't know how to interpret the readings, focusing only on the efficiency numbers and ignoring the critical numbers, and in most cases, wouldn't know what to do if the numbers were incorrect.
This is a case of technology outpacing the service industries ability to handle demand.
TIme for contractors to buck up and learn how to handle this technology, or don't attempt to work on the fireside of the equipment,,,
A smart contractor will specialize in this area and get his employees trained and properly equipped. You are allowed to charge a premium for specialty services...
ME0 -
I really am not
convinced that a correct total diagnosis was done.
I AM CONCERNED ABOUT SOME OF WHAT YOU POSTED ABOUT YOUR BOILER AND THE FINDINGS. SEE MY COMMENTS IN BETWEEN YOUR POSTING. Maybe not so bad Q90
Final chapter:
MAYBE NOT
Since my last post, I had a lengthily conversation with Scott Dam at ECR about the operational characteristics of the unit which was very enlightening. Scott is very knowledgeable and arranged a visit to my home by their Regional Sales Manager a person from their Technical Service department. Both of these gentlemen were professional, knowledgeable and I want to thank them for taking time out of their busy schedules to address my boiler issues. Also present was my heating contractor.Since my last post, I had a lengthily conversation with Scott Dam at ECR about the operational characteristics of the unit which was very enlightening. Scott is very knowledgeable and arranged a visit to my home by their Regional Sales Manager a person from their Technical Service department. Both of these gentlemen were professional, knowledgeable and I want to thank them for taking time out of their busy schedules to address my boiler issues. Also present was my heating contractor.
THIS FIGURE OF 11.3% IS ALMOST STOICHOMETRIC (PERFECT COMBUSTION) AS THE ULTIMATE CO2 FOR NATURAL GAS IS 11.7%. THE 11.3% IS VERY HIGH. WHAT WAS THE CARBON MONOXIDE READING AT THAT LEVEL?
guess he thought that was close enough. I adjusted the throttle screw down till the reading was 9.2, right center in the allowable range. This took about 6 turns of the throttle screw from where it was. It also reduced the burn rate from 200KBTUs to 175K BTUs as measured by the gas meter. There is no trail to figure how my 175K boiler got set to exactly 200K, so that still bothers me a bit, but it is correct now and will remain a mystery.
AS YOU ARE ADJUSTING THE THROTTLING SCREW TOWARD THE HIGH END OF CO2 THERE IS MORE GAS BEING PULLED INTO THE CHAMBER AND THE O2 (OXYGEN) IS GOING DOWN, I WOULD VENTURE THAT THE O2 WAS AROUND 2%, DID YOU TAKE AN O2 READING? THIS WOULD EXPLAIN THE INCREASED INPUT TO THE UNIT.
forever more.
I AGREE WITH SCOTT!
The throttle adjustment screw not only changes the mixture, but it also has a significant impact on the burn rate, enough to easily make my 175K burn at a 200K, and probably has enough range in it to go even higher, or lower I would suspect, all this while the flame “looks good”. The throttle adjustment screw not only changes the mixture, but it also has a significant impact on the burn rate, enough to easily make my 175K burn at a 200K, and probably has enough range in it to go even higher, or lower I would suspect, all this while the flame “looks good”.
A FLAME LOOKING GOOD (NICE SOFT BLUE FLAME NOT LIFTING OR ROARING) IS NO INDICATION OF PROPER COMBUSTION/
ACTUALLY THE BURN RATE IS NOT THE BIGGEST CONCERN BECAUSE AS YOU TUNE THE UNIT IN TO THE CORRECT READINGS THE CO2 WILL BALANCE OUT WITH THE O2 AND CARBON MONOXIDE SHOULD GO DOWN ALONG WITH FLUE GAS TEMPERATURE. THIS WOULD IN TURN INCREASE EFFICIENCY INDEPENDENT OF THE ACTUAL FINAL BURN RATE. YOU WOULD NOT REALLY SEE THAT INPUT ALL THE TIME AS THE UNIT WILL MODULATE THROUGH THE STEPS.
From a procedural perspective, to properly tune this boiler one needs to ensure the CO2 is set in the allowable range to start with and then go to the meter and carefully calculate the gas flow, adjusting the throttle screw such that the gas usage is also correct for the boiler size, while maintaining a CO2 in range. It takes both CO2 and gas flow to tune the thing properly and it takes one or two iterations back and forth between the gas meter and the CO2 meter to get both the CO2 levels and the gas flow usage correct. You must measure both. From a procedural perspective, to properly tune this boiler one needs to ensure the CO2 is set in the allowable range to start with and then go to the meter and carefully calculate the gas flow, adjusting the throttle screw such that the gas usage is also correct for the boiler size, while maintaining a CO2 in range. It takes both CO2 and gas flow to tune the thing properly and it takes one or two iterations back and forth between the gas meter and the CO2 meter to get both the CO2 levels and the gas flow usage correct. You must measure both.
YOU CAN DO THAT RUNNING BACK AND FORTH BUT WITH CORRECT GAS PRESSURE TO THE UNIT THIS SHOULD BE ABLE TO BE DIALED IN WITH THE THROTTLING SCREW AND THE COMBUSTION ANALYZER.
AS ONE WHO SPENDS A LOT OF TIME INSTRUCTING CONTRACTORS IT IS SAD THAT MOST OF THEM DO NOT KNOW THE BASICS AND THE FUNDAMENTALS OF GAS AND COMBUSTION AIR. MANY WHO POST HERE ON THE SITE ARE VERY WELL VERSED ON THIS BUT THEY ARE THE EXCEPTION BELIEVE ME; A LICENSE ONLY MAKES YOU LEGAL IT DOES NOT MEAN YOU KNOW WHAT YOU ARE DOING! THEN THEY ACTUALLY COLLECT MONEY FOR NOT KNOWING WHAT THEY ARE DOING.
My boiler was over fired, that is bad, but didn’t necessarily explain the intermittent shut downs. We then measured the gas pressure. The static pressure was 6.9 inches, but with the burner on it dropped to 2.5 inches which is below the 4 inch minimum pressure spec. My boiler was over fired, that is bad, but didn’t necessarily explain the intermittent shut downs. We then measured the gas pressure. The static pressure was 6.9 inches, but with the burner on it dropped to 2.5 inches which is below the 4 inch minimum pressure spec.
THIS IS WHERE I START TO HAVE SOME CONCERN. FROM READING THIS POSTING YOU HAVE A GAS METER AND A REGULATOR SO YOU ARE IN A HIGH GAS PRESSURE AREA. THE MAIN IN THE STREET PROBABLY HAS 50 TO MAYBE 100 POUNDS PRESSURE. THERE IS NO WAY YOU SHOULD EVER HAVE INSUFFICIENT PRESSURE. NOW GRANTED YOU MAY HAVE HAD A BAD POUNDS TO INCHES HOUSE REGULATOR BUT SOME OF THE NUMBERS YOU REPORT ARE A PROBLEM TO ME. I ASSUME WHEN YOU SAY STATIC PRESSURE THAT WAS TAKEN WITH NO EQUIPMENT OPERATING? THE PRESSURE AT THE EQUIPMENT SHOULD BE EXACTLY THE SAME AS IT WAS AT THE OUTLET OF THE REGULATOR WITH NO DROP IN PRESSURE!
THE 7 INCHES IS THE STANDARD SETTING FOR A HIGH PRESSURE POUNDS TO INCHES REGULATOR. THE 4.5 INCHES AT THE BOILER IS A PROBLEM AS YOU HAVE A 2.5 INCH W.C. PRESSURE DROP WHICH IS WAY TOO MUCH, YOU SHOULD HAVE 7 INCHES AT THE BOILER.
STILL A PROBLEM IT SHOUD BE 7” EVERYWHERE YOU ARE LOSING PRESSURE SOMEWHERE.
YOU NEED TO HAVE AN UNINTERUPTED ¾” PIPE ABOUT 10 FEET LONG GOING DIRECTLY TO THE BOILER AT LEAST. THE GUY FROM THE GAS COMPANY NEEDS TO DO A PIPE SIZING CALCULATION FOR YOUR ENTIRE SYSTEM.
I AGRRE BUT WHAT FOLLOWS I DO NOT AGREE WITH.
IN A HIGH PRESSURE AREA IF YOU HAD THAT TREMENDOUS A PRESSURE DROP IN THE DEAD OF WINTER ON THE COLDEST NIGHT THEN THE PIPE IN THE STREET IS DRASTICLY UNDERSIZED THIS IS ALMOST IMPOSSIBLE WITH HIGH PRESSURE GAS SYSTEM. I JUST DO NOT BUY THAT FINIDING AT ALL.
I HAD A ONE WEEK CLASS THIS WEEK ON ALL THIS TYPE OF IMPORTANT FUNDAMENTAL TRAINING. THE CLASS WAS ATTENDED BY ONE MAN. MOST TECHS COULD CARE LESS ABOUT LEARNING THEY ONLY WANT TO GET PAID AND GET OUT OF THE HOUSE. SORRY YOU HAD TO EXPERIENCE THIS. IT WILL EVENTUALLY RUIN THE HYDRONICS BUSINESS IN AMERICA.
A GOOD COMBUSTION MAN DOES NOT NEED TO LOOK AT THE FLAME HE NEEDS TO LOOK AT THE INSTRUMENT TAKING COMBUSTION READINGS AND THEN KNOW WHAT TO DO WHEN THEY ARE NOT CORRECT.
In conclusion, I would apologize to the folks at ECR for some of the abuse I have dished out in this post about the unit, even though these posts are what it took to get enough attention and people here who knew what they are doing. Understand my frustration had reached the breaking point because I believed the heating professionals I was working with understood the unit. In the end their knowledge was only casual and insufficient to see the “big picture” or even the little details. The good folks at ECR came through with an onsite visitation from two very qualified people, Don DeCarr from Technical service and Robert Shea, the Regional Sales Manager (here in NY), both of these gentlemen went out of their way to come to my home, were very professional and knowledgeable as was Scott and I appreciate their time, effort and expertise. Thank you to EC for allocating the necessary resources to get my problems resolved.There is also a discussion to be had about cleaning and flushing the unit, and if the unit is in condensing mode or not which tends to have a flushing effect on the oxides if it is, but I’ll leave that discussion to someone else.
THE TRUTH IS MOST OF THESE FACTORY PEOPLE ARE TOP OF THE LINE CONCERNING THEIR OWN PRODUCT AND ARE TO BE COMMENDED. IT IS ALWAYS INTERESTING TO ME WHEN I READ A POSTING AND THE TECHS AND HOME OWNERS WANT TO BAD MOUTH THE PRODUCT. MOST REPS I TALK TO TELL ME THAT 90% OF THE PROBLEMS THEY FIND WHEN MAKING A CALL IS THAR EITHER THE INSTALLER, OR SERVICE TECH DID NOT FOLLOW PROCEDURE. THE NSTALLATION AND OPERATIONS MANUAL IS TO SET THE COFFEE AND SODA ON!
The quote
"I HAD A ONE WEEK CLASS THIS WEEK ON ALL THIS TYPE OF IMPORTANT FUNDAMENTAL TRAINING. THE CLASS WAS ATTENDED BY ONE MAN"
scares me. Anyone else agree?All Steamed Up, Inc.
Consulting0 -
Scary
Scary indeed! I only wish Timmie's training center was closer!0 -
Well
maybe we can get a few people together for a trip to Providence and split the driving.....All Steamed Up, Inc.
Consulting0 -
Now THAT is one VERY fortunate student....
I hope he was sponge like and soaked up all of TIm's knowledge. Talk about an opportunity of a lifetime...
This echoes what I said in my post. Not many people interested or skilled in how to do it right.
ME0 -
I would love
to have all of you come, we would have a ball!
Might I say concerning only having one man in class, some have said they would not bother with one man classes. Well I have done many of them simply because one I really love what I do, two if that one person is willing to come and listen to me for 40 hours I will go out of my way to accomodate. I was blessed with my student this week who was very eager to learn and he pulled the information out of me with his questions and involvement. The one on one is great as I can give him my undivided attention.
I always say I may not make a lot of money but we sure are having fun. You really have to love this stuff.0 -
Final chapter
Hi Tim, Thanks for your excellent feedback, Ill respond to some of it here.
Regarding
The manual calls for 8.5% - 10% CO2 so I guess they want set at a non Stoichometric level. I set mine in the middle to 9.2%, CO at this setting was 37ppm and. The CO before reducing the setting was much higher; I don’t recall what it was.
The O2 is now 4.7% which is between the 2% - 5.5% recommended. I didn’t take the “before” reading on O2 .
Exactly correct, and a very important point, these things aren’t your grandfather’s boilers, as I said, barely a noticeable difference in fame characteristics between before and after conditions. I’m no expert, but based on my limited experience that if one noticed the flame is out of whack on one of these things then the unit would most likely be very, very far out of combustion spec.
Interesting point Tim, but in adjusting the throttle screw to modulate the CO2 / O2 readings does effect the burn rate, and quite significantly. In my case dropping from 11.3% to 9.2% reduced burn rate by 25K BTU’s. I understand your theory, but based on the instructions I disagree with you on this point. The instructions clearly say to set it up such that the CO2 / O2 are within the allowable ranges at the correct burn rate level for the unit, which in my case is 175K BTU’s. Based on these instructions the calibration is keying off of the burn rate as the “fixed” reference and asking for adjustment of the other settings to be within spec while converging them at the specified burn rate. What did you mean by “Modulate through the steps”?
That’ s a great idea, I’m not an heating expert as you may have guessed, so please explain how to measure input BTU’s with the combustion analyzer, cause I’m tired of running back and forth!
Yep, the pipe is too small from the main feed to the boiler, “they” used ½” pipe, hence the pressure drop. I’m going to change the pipe even though I now have above the min of 4in of gas pressure to the boiler.
Yep, I know, but lowered pressure fits ALL the failure symptoms, could have also been my regulator where even a small pressure change in the city pipe would result in a sympathetic change in the house pressure. Remember, I only had 2.5 at the boiler on a warmer day, which is already below the minimum of 4 required by the boiler and that didn’t take into account if the dryer or oven was also on so it may have dropped even lower at times. At some point the boiler will start to have issues, and without testing for it at various pressures I don’t know exactly what that min level is. So, if you have another theory to fit my failures, I’d love to hear it but for now, and certainly after I replace the pipe, this is all I got. Believe me brother, if after I change the pipe and it fails again, you’ll be the first to hear about it and I’ll be glad to accept your “told you so”…!
Thanks for all your great comments Tim, and on the above I’ll add my own to yours. You said A LICENSE ONLY MAKES YOU LEGAL IT DOES NOT MEAN YOU KNOW WHAT YOU ARE DOING!
I spent more than a few years training people in electronic equipment, operation and calibration. This was very complicated and expensive gear ($100K+) and what we learned is that if we allowed somebody to represent our equipment and company through selling and servicing our products they had to know what they were doing.
I will never buy an installed system again without first verifying the training credentials to the company/technician who wants to sell it to me.0 -
About to purchase the Q90-200
I'm about to replace my 25+yr NY oil boiler in my house. I'm at the crossroads to decide whether to switch to gas, or stay with oil. I'm leaning towards gas and have zeroed in on the Q90-200 model along with an 45 gal. SS indirect water heater. I've tried to read the various comments on this boiler and I think I'm basically where I was when I started...undecided! I'm looking at getting it installed through Sears, along with the master protection plan, so I'm hopeful that issues surrounding the install, follow-up service, shelling out addtional $$ will be a non-issue. So, I guess I'm looking for some confirmation about this unit and it's efficiency and reliability before I put out some serious $$. Based on what my current boiler's AFUE is (the guestimate is somewhere in the 50 or 60% range) whether I go with oil or gas, I'm saving money. I'd like to really maximize on the gas savings though, so I'm hoping the Dunkirk 90-200 is going to be a realiable boiler. Thanks for your thoughts.0 -
I'm looking at getting it installed through Sears, ...
"I'm looking at getting it installed through Sears, along with the
non-issue."
Since I am not a professional, I cannot advise you on what boiler to get, or whether to convert to gas or not. What I can advise is that it is vitally important that the installer, and the follow-up services be provided by someone who is really competent and has the required tools to do the job. In my estimation, this is more important than the relative efficiency between one boiler and another. I imagine you would have a tough time rating the quality of workmanship from a place as large as Sears. You might never get the same technician two times in a row. You would certainly want to interview some of their customers after they have had their heating system for 5 years or more, and even then, that would just rate the subcontractor(s) they happened to get. It strikes me that it would be about the same as having the gas company do the install for you.
A friend of mine used to be a tech for them. He got to work on everything: window air conditioners, washing machines, dishwashers, refrigerators, microwave ovens, ceiling fans. He was a clever guy, so for all I know, he did a good job on those. But he was not factory trained on any of that stuff. I doubt he did oil or gas appliances.0 -
Q90 Decision
Q90 Decision
I’ve had a long road with the Q90 and here is what I found out.
These new High efficiency systems like your old unit. In the past a boiler was lots of iron, a big fire and let it rip. If the combustion settings were even close you had fire, heat and/or hot water and little or no intelligence in the system to know the difference or even care, fuel was cheap and the fire box was big!. Not so with the new high efficiency condensing systems, these units are pushing the envelope of material design and control systems as such they demand near perfect combustion parameters, sufficient inlet gas pressure and carefully laid out intake and exhaust venting.
A failure to install the unit correctly which means giving the proper consideration to exhaust vent and intake pipe layout to balance pressures and ensuring there is proper gas inlet pressure as starters can lead to intermittent shutdowns of the combustion system. The unit is impossible to set up correctly without the use of a combustion analyzer. No amount of experience can yield the correct adjustment by looking at the flame, shape, size and color; it must be done with the instrument.
I say this from my own experience. The plumber did a poor job of exhaust vent piping layout. It caused a standing pressure wave to set up an oscillation in the exhaust vent. This would cause the pressure switch to shut down the unit, sometimes, depending on among other things, weather! He also didn’t check the gas inlet pressure; it was below the spec for min pressure and could have also caused my intermittent failures. He didn’t use a combustion analyzer to set it up; he used his “eye”. When I finally checked the combustion specs using a combustion analyzer I found that my 90% boiler was running in the low 80’s, CO was way off as was CO2, and when checking the gas flow rate the unit was over fired by 50K BTUs, it is a 175KBtu running at 225KBtu.! The thing was a mess.
All this took me over 4 years to get sorted out despite numerous and costly service calls to the heating person who I thought knew what he was doing, turns out he had no idea. As of half way through last winter, the system appears to finally be under control and ran fine for all the second half of the winter. I’m looking forward to my first COMPLETE winter of heat this upcoming season, year 5!
So, the reason I took the time to say all this is if you buy the Dunkirk or other HF boiler, installation and setup is everything! Anybody can come to your house and charge you for changing parts after the warrantee is over, but only a few people really have the insight to install and set these things up correctly. Finding a qualified, trained heating technician is your mission and given the cost of a service call, I would not worry about a few hundred dollars of price difference between the qualified person and the lower cost person who may not be as qualified/trained.
I should also mention the people from Dunkirk who in the end were very helpful in finalizing the last few issues with my system and helping me to get them cleared up, all of which were installation and set up issues. They took a lot of abuse in some of my posts and I thank them for stepping up to get it sorted out., even though my problems were not product related problems. I’ll drop a post here this winter to let you all know how things are going with the unit now that we believe all issues have been addressed, hopefully it will be a cheerful one!0 -
washedup
I am the sorry owner of 4 failed Lennox complete heat systems and two failed Dunkirk Q90 series boilers( my house is only 13 years old). I am not conversant in the techincal explaination for all this. All I know is I'm cold, without hot water and needing to spend more money to fix something everyone else knew would never work anyway.If the Q90 boiler were a car, we would call it a lemon... SO...where is the sign up for a class action? I would like to join.0 -
Multiple problems
Am I to understand that in 13 years you have had multiple boilers installed?
Have they all been installed by the same installer?
There seem to be several common threads running through your unfortunate situation:
Flue venting
Gas supply pressure
Electric wiring
Installer
Could any of these when installed improperly have caused your problems?
Sometimes if too much effort is put into blame, there will not be enough energy for problem analysis and correction.--nbc0 -
It aint easy
Hey "washed up",
My experiences were similar, until l took matters into my own hands and worked to understand how the boilers work and to get it straightened out. Here is a brief summary of what I found out.
First, don’t trust your heating contractor just because he is a heating contractor. My contractor had many years of experience on conventional boilers, but absolutely did not understand the subtleties of these high efficiency boilers And how important it is to pay strict attention to the set up specs.
In brief, here is the list of installation problems in order of their discovery and some adjustment problems I resolved on my system over the course of 5 years. If you read my earlier posts you may be able to tell that I was a little teed off about the whole thing, I’m better now, so far. In retrospect, these should have been taken care of upon installation, with the exception of number one, as it turned out to be a little tricky and not easily perceived.
1. Exhaust venting was problematic even though the length and number of elbows was in spec. On the intake and exhaust there were two 90 degree elbows, the sharp kind, not the sweeping kind, located about 2.5 ft from each other. The symptom was my boiler would shut down for no apparent reason. A local field rep noticed my exhaust was “Puffing”, lots of little ones, and then a big long one, then the pattern would repeat. His theory was the two 90 degrees separated by such a short distance was setting up a pressure wave oscillation in the exhaust piping. Sometimes the pressure would build up to a point (the big puff) and occasionally the differential pressure switch would trip and cause a shut down. We corrected the problem by installing the gradual sweep elbows and the intervals between shutdowns increased dramatically, but were not eliminated. The puffing went away.
2. Combustion set up. Rule number on these things is you cannot tell by the way the flame looks how well the combustion is set up. My flame looked great, not orange, beautiful little blue guys on the combustion tube, very nice. In reality by 200K boiler was over fired by close to 250K BTUs! It was over fired by 25%. I noticed this first by reading the manual and counting the meter as it describes. I put a combustion meter on it and sure enough it was way out of whack, so I adjusted it into spec. It took 7 full turns on the throttle screw to bring it down. This reduced the shut down interval still further, but did not eliminate it. My heating contractor used his eye to adjust the flame, at the time, what did I know? Silly me.
3. In year 5 or so the unit started shutting down due to a low water condition, except that there was no low water condition, but the sensor thought so and would intermittently shut down the unit until one point where it wouldn’t even start up any more. Turns out the sensor is the electrical type, a probe 2-3 inches long which senses the current and without water, there is no current flow so it shuts down. When we pulled it out, it was coated with some brown/black film effectively acting as an insulator and preventing the sensor from getting the correct signal. We cleaned off the sensor probe and that fixed the problem.
4. The high temperature switch caused a shut down twice, not sure why, didn’t happen again
5. Lastly, is the gas pressure, the unit requires a minimum amount of pressure to operate. My pressure measured at the main pipe feeding the down pipe to the boiler cabinet was fine. The pressure at the bottom of the down pipe was lower and the pressure and after the pipe goes into the cabinet and through the little piping that Dunkirk supplies there was another drop as measures right off of the valve. So, three pressure drops and the last one was below the minimum specification. We changed the drop pipe to a larger diameter, changed the elbow going into the boiler to a larger diameter and upped the pressure on the gas regulator a tad coming into the home. The result was a pressure, while the boiler was running which was above the minimum specification. Note: it is important to measure the pressure at the valve with the boiler running and some other gas appliances on. The combustion was re tested after the gas pressure was corrected
The above tale is spread over 5 painful years, I had spoken to the factory reps near the end and had two of them come out to review the installation last March or so. Since the last fix, which was the gas pressure issue, the unit has not shut down once. The factory reps reviewed the installation and it did not require any additional modifications. I am fully expecting this unit to operate without failure, with the exception of normal wear and tear on what is not a 7 year old boiler.
In the end I received great support from Dunkirk and great input some of the people on this board, but as I said, don’t assume you heating contractor is taking the care required to properly install and set up these new high efficiency boilers, they are not like the “Old “ ones.
Good luck0 -
It aint easy
Hey "washed up",
Good luck0 -
bad boiler
I deal with so called bad condensing boiler on regular basis, and still have to find one bad boiler. i did not read this tread completely, but i did serviced those boilers which was giving homeowners problems for years, and i always see on problem: unqualified technicians not reading manuals and not having proper tools, All those condensing boilers are marvels of boiler technology and fail due to poor installers.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
Thank you for bringing this thread to a meaningful conclusion
Thank you mssrs. Badq90, and grennady for clearing up some of the misconceptions in this very long thread.
As one has said,"you don't get what you didn't pay for". And professional expertise is one of those things which many supplicants here realise they have missed.
We all need to realise that we are not buying blue jeans here when we buy a boiler, but rather a professional service of which the boiler selection is a minor part.
Would we choose a doctor because he advertises kidney transplants for less? Would we choose a politician because he promises a Volkswagen in every garage?--NBC0 -
Dunkirk Q90-100 Short Cycling
I have a Q90-100 that is shutting off after reaching 120 degrees. I disconnected the air intake going outside, and now it shuts off after reaching about 150 degrees. The Boiler Control (IBC) is brand new. Igniter is about a year old. When it shuts down the power light on the IBC stays on, so it can't be the casting temperature safety switch. I've set the High limit Aquastat to 200 degrees instead of 180, but this did not work either. I've ruled out simple problems like the room thermostat.
I'm looking for a technician in the New York City area familiar with the Quantum series gas boiler. This may seem like a simple request, but in the 10 years I've had this boiler it's never run right no matter how many service people came to look at it.
Joe0 -
New thread?
If you get no replies today, then repost with a new thread, as your post may get lost at the end .--NBC0 -
Q90
Try clearing the furnace drain. I had to flush a q90 heat exchanger today.0 -
Where in NY
I'm in Westchester.There was an error rendering this rich post.
early cut off
Joe,
I’m no expert, or a plumber, or a heating contactor, but have lived a bit with a Q90. Here is my theory: Removing the intake pipe changed the amount of flow restriction on the intake, lessening it most likely. Given that this had an effect on the shutdown temperature I’d suspect that the reason it is shutting down is due to the differential pressure switches exceeding their limits, and may have nothing to do with the actual temperature you are reading. This explains why the aquastat change had no effect and the reset switch doesn't trip
This type of premature pressure induced shutdown can happen because the intake pipe is restricted, or exhaust side is restricted. Inclusive on the exhaust side of the equation is the exhaust pipe itself being clogged and the grate in the bottom of the boiler being clogged. If the grate gets clogged, it will increase the back pressure just as if the exhaust pipe was clogged, the pressure sensors detect this and shut down the unit. From the human perspective, it looks like a random, unexplained shutdown. When you removed the intake pipe you increased the airflow flow rate and therefore the pressures were a little more happy for a bit. As “HVAC Tech” stated previously, if you haven’t had the unit serviced where they remove the burner and flush/brush the built up crud out the grate, you have to do that. The exhaust goes through this grate and if it is clogged, it builds up back pressure and can trip the switches.
Good luck0 -
dunkirk Q95 problem
I have a customer that purchased a dunkirk Q95-200 boiler in 2007. He purchased it himself (bought it on-line), and installed it himself (are you scared yet?). The boiler is fired on LP gas. I don't want to sound like Mr. Obvious here, but he has had issues with the boiler since installed. He had a plumber come out and look at it a few years ago and according to the customer he (the plumber) replaced the draft inducer and the burner. I met this customer a couple of years ago when we started to service the commercial HVAC equipment at the machine shop he owns. The customer says the boiler will BOOM so loud occasionally that it will wake him and his wife up from a sound sleep. We went out to the customers house today, looked through the installation manual and compared his install job to the manual and what we do when we install boilers. He put unions in the 3" intake and exhaust pvc pipes, he put the expansion tank and city water fill on the supply side of the pump, and his zone valve wiring was fuctional but a little "cave" .
We hooked a combustion analyzer up to the unit and ran it in low and high fire. We made minor adjustments to the throttling screw to bring the unit within the specs provided in the book.
We ran the unit through numerous cycles and it lit and ran very smoothly and quietly. The customer said the "booms" seem to happen at night. He also said his house has a hard time heating up on mild days (OK when very cold out). I went into the parameters to check for outdoor air reset problems and when I exited from the parameters a E-38 fault code appeared (no E-38 code in the manual). I called the factory for assistance and they said they never heard of E-38 fault code and said if I accidentally pushed a wrong button while in the parameters I could generate a fault code that could not be field repaired. The factory recommended I replace the board. I now have a new board coming.
I need to very clear here. I am not a BPI (button pushing idiot). I very slowly and methodically reviewed the parameters (I've run too many service calls mopping up behind BPI's). If I did accidentally push an incorrect button, why can I not get back into the parameters to look for damage. How can they (Dunkirk) build a product to these specs. We are TRANE dealers and if TRANE were to do something like this they would send a new board under warranty and want the old board back to investigate the issue and make changes to future boards.0 -
There is a lesson to be learned here
I've followed this thread and what I get out of it is the Q90, and many other ultra efficient boilers, are extremely fussy about having all the I's dotted and T's crossed when it comes to installation and set up. They are unforgiving and should only only be installed and maintained by experienced factory trained techs who have installed many of them. Those type of people are apparently hard to find - chicken and egg thing.
I'll be replacing my steam boiler this spring and I will not even look at something like this. If I were going to stay with oil I'd go with the Megasteam but because I'm probably going to go with gas I intend to use the Smith series 8 with a Carlin gas gun in it. Both boilers are top of the line and do not rely on electronic controls to achieve the last few percentage points on efficiency. Too many of these uber efficient setups are just to complex to work reliably so anything you save in fuel you will give away in spades on service calls unless you are extremely lucky.
Someday these new systems will work just fine but I think that day is not here yet. I've been burned by adopting new technology to soon in other areas. Don't volunteer your house as a test bed for the latest and greatest, let others be the canary in the coal mine.
Back when i used to design power supplies for a living I learned one VERY important lesson. KISS - keep it simple stupid.
3PSI gauge0 -
But what if?
"Back when i used to design power supplies for a living I learned one VERY important lesson. KISS - keep it simple stupid."
I designed stuff a little like that for government clients. They were extremely fussy. If you did not agree 100% with the specification, they would not even consider your bid, nor would they discuss it.
So we would get an RFP for a DC power supply with 0.01% accuracy in output voltage from -55C to +85C at the load. Well, we might be able to do that if we could get a voltage reference that would do that, but we could not. And we would need to run two heavy wires to the load to deliver the voltage, and two smaller ones back to the power supply so it could see what the load was seeing. They would not tolerate the extra two wires, so we no-bid that job. But where would we get a mercury standard cell that would run over that temperature range? And that would not break when exposed to MIL-E-5400 Class H shock and vibration testing? (This was in the early 1960s.) Zener diodes would make more sense. Their loads did not require anywhere near the accuracy they demanded, but they would not hear that. So they probably got something very complex to solve their problem, if it did. Even though they proclaimed they had a K.I.S.S. program in effect. But they sabotaged it right at the beginning at the specification writing stage. We no-bid a lot of RFPs for things like that.0 -
CYA trumps KISS every time
Program managers are to concerned with CYA to pay any attention to KISS.
We found that a face to face meeting could alert you to possible problems of this sort and you adjusted your bid accordingly. We always told them we could build just about anything they could afford.
After my job went to China, I worked the last 8 years of my working career for the USPS repairing mail processing equipment. Every single machine was a prototype; the manuals and schematics were suggestions of how the machine could be built. One extreme to the other.
3PSI gauge0 -
I remember an especially bad RFP.
The military really wanted an excuse to keep a computer they had, but did not dare say so. So they put out an RFP for a system to read a lot of strain gauges. They specifically did not allow signal conditioning amplifiers at the output of the strain gauges, but insisted on a multiplexor and specified a fancy signal conditioning amplifier after the multiplexor. That was not likely to work. We designed and built solid state multiplexors, but we could not use them on this job for two reasons: the noise in the multiplexors would be too high, and their specification specified a relay multiplexor.They did not name the multiplexor, but only one company made one that would meet most of the specification. It used reed relays with gold plated contacts. It just might work. The government specifciation was a copy of the relay multiplexor company's product, even the spelling error. But one line was added. It specified that the contacts be mercury wetted. Now the multiplexor company did not use mercury because that would make a battery (mercury on gold) that would spoil the noise level. Specifying mercury wetted contacts guaranteed that the noise level would be too high to achieve the other requirements. I tried to explain this to the contracting officor, but he said I did not know anything about government contracts. So another job we did not bid on.
The funny thing is that after I left that company (on friendly terms) and worked for another company, I got a call from the former employer. They got another RFP from the same agency for the same system -- this was perhaps two years later. They wondered what they should do. I asked if the item about the mercury wetted relay contacts was still in there. They said yes, so I said not to bid on it again.
The government obviously wanted a fancy noise generator that would keep the computer busy trying to rescue data from the noise that their RFP required.
Your high taxes at work.
.0 -
Quantum 90 Junk
The Quantum 90 is not a good boiler. We built a house 3 years ago and had one of these installed the first one sounded like a leaf blower in the basement, I was told that it was normal, after complaining about it enough it finally got replaced come to find out there was a hole in the casting causing this. The second boiler that was installed has stopped working at least a dozen times, I'm sick of service calls. For what I paid in service calls I could of paid for most of my next boiler. This unit is a piece of junk they should take it off the market. I have contacted Dunkirk and never got a reply, I will probably have to junk this and get another boiler. I will not go with a Dunkirk again, would not recommend them to anyone.0 -
Did You Miss the Name of This Site?
It's not "Consumer Complaints" or "Maligning Manufacturers" or "Ridiculous Ranting". It's "Heating Help". Its purpose is just that: to give help to people with their heating systems.
It's apparent that you did not come here for that purpose since you haven't provided any particulars about whatever problems you may be having, nor have you ask any questions as to how to correct anything.
I also doubt that you read the post that you linked onto because if you had you would have seen that all the others who complained about their Dunkirk boiler later came to find that the problems were the fault of their installer/servicer and not Dunkirk's.
If you want help, then post what your specifics are and ask questions. If you only intend on bashing the manufacturer, move on. That is not the purpose of this forum.Bob Boan
Lemon in da house
Settle down francis. The question was- Has anyone had problems with Dunkirk Boilers? Absolutely! Nothing but problems with Dunkirk for the last 5 years. I am thankful to see this thread so I know that I am not alone.We've had problems for 5 long years. The first 2 years it was replaced 2 times. Maybe three, I can't recall anymore. I'm over it. I'm a mom of a little girl and a baby boy. Currently we are freezing with snow in the forecast and this POS has taken a fall once again at 9pm at night. I can and will say with complete certainy that Dunkirk sucks. End of story. I will never go another day nor night with having my children cold because I decided to use an inferior product and I hope this thread helps others decide to not go with this Dunkirk so they don't throw there money away as well.0 -
What to do about the problem boiler
Have you contacted the original installer?
His work on the boiler, or a lack of maintenance may be more to blame than the manufacturer of the boiler.
Is your boiler new to you in a new house, or was it installed by someone you chose?
If you had your tire repaired, and it afterwards fell off, would you blame the tire manufacturer?--NBC0 -
DUNKIRK PSB-4D
I have purchased a new Dunkirk PSB-4D bas boiler at the end of September of this year oand had problems with it from day 1. I froze more days than I had heat. The contractor & Sears (whom I bought from) said there is nothing wromg. I called my local gas company and was told that the problem is a cracked boiler. I am still waiting for someone to come and repalce it,0 -
DUNKIRK PSB-4D
Dunkirk-sears problem
Why not start a new thread here with pictures of your installation, and a description of what seems to be wrong. This thread contains so many post, that yours will be lost.--NBC.0 -
Dunkirk Q90 cracked block
I fully renovated my house 5 years ago. Within a year I noticed a leak near my boiler, but I thought it was coming from somewhere else. Turned out it was a cracked block. Got a whole new unit sent to me, but I had to pay $1200 to install it! Now, less than two years later, the same thing has happened! Water on my basement floor and a wet spot on the block. I can not believe I am here again with this unit. Dunkirk clearly has a problem with their casting process. As an architect I will never recommend this brand to my clients. Fool me once. Once my Q90 is assessed by my HVAC consultant I will attempt to get a refund. I'm sure Dunkirk will deny me as they did in the past. I will need another boiler, just in time for the holidays. Any recommendations?0