Feet of head
Techman
Techman Member Posts: 2,143
How do you figure a circulator's "head " when the linear feet of pipe is close to 900'- 1000' with a flat plate heat exchanger at the end ? total length x .06 and then what? This is a chilled water system. And what is the GPM thru 4' PVC ?
  • Ironman
    Ironman Member Posts: 7,857
    GPM?
    We need to know how many GPM you're trying to move to begin the calclation.
    Bob Boan
  • JStar
    JStar Member Posts: 2,752
    The HX manufacturer should give you a pressure drop.
    You can run any number of GPM through any size pipe. It's just not always practical...or quiet.
  • Techman
    Ft of head
    The circulator is supposed to move 500 GPM. Pressure across the circ is 20psi return and 42psi supply. I will have to get the heat exchange info. Thanks!
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875
    WYSIWYG...
    What you SEE is what you GET...
    Obtain the pump manufacturers performance curve. You MUST know the "trim" that the impeller received, if any.
    Convert PSI seen across the running pump to feet of head because that is what all manufacturer use in their charts.
    There are 2.307 feet of head per 1 PSI. So in your case, 22PSI X 2.307 = 51 feet of head. Enter the manufacturers curve on the left vertical at 51 feet of head, and move across until you intercept the slope of the performance curve, then drop straight down and read the GPM being moved for that given condition. I doubt that you have any flow variables on a cooling tower, so WYSIWYG.
    As far as what it is SUPPOSED to be seeing flow rate wise, that is usually called out by the chiller manufacturer. I know there are some rules of thumb out there as it pertains to flow per ton capacity, but have never used it before. I always depend on reliable (manufacturers) requirements as opposed to R.O.T.
    HTH
    ME