sizeing radiation
Dan467
Member Posts: 11
If i have the edr of a convector suplied with 180 degree water how do i convert it to btu output 0f a boiler? Also sq ft of radiator to btu out put?
Multiply...
The square footage x 150 for the btu output at 170* average water temp. The boiler will generally have 3 ratings: input; output (input x efficiency); and I+B+R (output x .85). This final number allows for a 15% piping loss. Actual loss may be more or less depending on piping material, length of run, pipe insulation, water temp, etc.Bob Boan
sizing radiation
thanks for the sq foot info how about edr?0 -
EDR
At 180 degrees, each EDR equals 170 BTU's.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
- 87K THE MAIN WALL
- 114 Chimneys & Flues
- 106 Geothermal
- 982 Plumbing
- 388 Solar