Pumping Away with the Prestige Solo 110
Helder
Helder Member Posts: 1
Hey everyone,
I'm having trouble visualizing the "pumping away" setup with the Prestige Solo 110. As you may know, it comes with the Grundfos pump and unless I plumb the feed line/expansion tank to the return side, how can it get done? I guess you can pump through the heat exchanger.
This system is going to use only the on-board circulator for heat and will have another circulator for DHW.
I'd love to get thoughts from all familiar with the Solo boilers.
Thanks!
edit: added info on circulators
  • Ironman
    Ironman Member Posts: 7,872
    More Info is Needed
    We would need to know about the size and length of the piping to your heating zones as well as the type of emitters you have. The on-board circ is sized to match the gpm and head of the boiler (10 gpm @ 10ft head). It is probably not sufficient to also carry your heating loop(s). This why the boiler should be piped in some form of primary/secondary fashion. In that scenario, the expansion tank would be in the primary loop, not the boiler loop, and the boiler circ would not be effected by its placement. See the attached application manual.
    Bob Boan
  • CMadatMe
    CMadatMe Member Posts: 3,086
    Return
    Exp tank and feed would go on the return. You need to calculate the required system head and included the boiler head to make sure the 15-58 can do the job. Was just on a job today where boiler kept going off on intermintent lockouts due to high limit just for this reason. While the manual shows a diagram it also states all over the place that pri/sec is recommended...Personally would use a low loss header rather then pri/sec.
  • R Mannino
    R Mannino Member Posts: 441
    Pumping Away
    just as Mr. Holohan. suggests.
  • scott markle_2
    scott markle_2 Member Posts: 611
    pumping away
    Viessman wants you to pump into their mod cons.
    With all respect to Dan and Gill if we get the expansion tank in the right place and we use a good quality air illuminator (spiro vent, etc.) does this real mater very much?
  • R Mannino
    What Matters
    is the location of the circulator.