                    Member Posts: 17                
            
                        
            
                    What are the 3 factors that determine the capacity of a TXV?                
                0                
            Comments
- 
            TXV
Are you talking theoretically? Or are you on a service call w/ a system that has a problem because the TXV is r22 and the comp is r134a and the Walk-In is warm because the TXV is not feeding enough freon?!0 - 
            TXV Capacity
i am talking theoretically0 - 
            Which
ones do you know about?0 - 
            capacity modifiers
1. Differential pressure across the TXV.
2. Subcooling of the liquid.
3. Superheat at the coil outlet.00 - 
            Expansion Devices TXV
The three factors that determine the capacity of a TXV are0 - 
            Expansion Devices TXV
The three factors that determine the capacity of a TXV are0 - 
            Epansion Devices
The three factors that determine the capacity of a TXV are theoritically0 - 
            This sounds like a test......:-)
I'll say Orifice size in valve, Delta" P" between hi and lo side and The temp and state of the liquid entering the valve...........
I took a shot. It's been a while since theory racked my brain......
Peace
Mike T.............0 
This discussion has been closed.
            Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements