TXV capacity

What are the 3 factors that determine the capacity of a TXV?

Comments

  • Techman
    Techman Member Posts: 2,144
    TXV

    Are you talking theoretically? Or are you on a service call w/ a system that has a problem because the TXV is  r22 and the comp is r134a  and the Walk-In is warm  because the TXV is not feeding enough freon?!
  • edow
    edow Member Posts: 17
    TXV Capacity

    i am talking theoretically
  • Techman
    Techman Member Posts: 2,144
    Which

    ones do you know about?
  • Tom Blackwell_2
    Tom Blackwell_2 Member Posts: 126
    capacity modifiers

    1. Differential pressure across the TXV.

    2. Subcooling of the liquid.

    3. Superheat at the coil outlet.0
  • Diamonds1
    Diamonds1 Member Posts: 3
    Expansion Devices TXV

    The three factors that determine the capacity of a TXV are
  • Diamonds1
    Diamonds1 Member Posts: 3
    Expansion Devices TXV

    The three factors that determine the capacity of a TXV are
  • Diamonds1
    Diamonds1 Member Posts: 3
    Epansion Devices

    The three factors that determine the capacity of a TXV are theoritically
  • Empire_2
    Empire_2 Member Posts: 2,343
    This sounds like a test......:-)

    I'll say Orifice size in valve, Delta" P" between hi and lo side and The temp and state of the liquid entering the valve...........



    I took a shot.  It's been a while since theory racked my brain......



    Peace



    Mike T.............