zone valve
catman
Member Posts: 8
having trouble with zone valve on two zone system one zone is getting heat other is not replaced motor and manually open valve still nothing could valve be bad?
Zone Valve
What is the brand name of the zone valve?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
zone valve
honeytwell0 -
Honeywell
I've never seen a Honeywell valve go bad, but you may need to drain the system, remove it and check it out.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Honeywell
can fail. Usually just the actuator motor, but I have seen them where the ball had swollen so much that even open there was no flow. That was one that overheated. With those, even though you manually open them, you need to turn up the other zone to supply heat to that one also. Could the zone be frozen, air-bound, or a valve shut off down stream? Is the circulator running, and what is the pressure on the boiler?0 -
zone valve
yesterday valve manual overide opened and finally got heat to come up does that mean the valve is sticking but still need to be replaced. the manual lever to open valve has no resistance when motor is in, when i disconnected the motor wire and then move the lever there was resistance then you could here the zone valve make a noise like it was opening but heat didnt come through zone till two days later.0 -
sounds like
the valve is working fine, but you are possibly getting gravity feed heat due to a bad end switch, circulator, control, or lack of boiler pressure. I don't think it was frozen.0 -
zone valve
i was talking to a plumber and he mentioned some thing about bad end switch and that would cause the valve not to open manually. is that replaceable without replacing whole zone valve. if it does need replacing is there a better zone valve to replace it with because this is not the first time had trouble with this one.0 -
Honeywell zone valves
can have the entire head replaced, or just the motor or just the end switch. However in your case I think you may want to have someone take a look at the valve body itself to make sure the internal ball is free wheeling and not stuck or damaged. If you go that far just put in a new valve completely.0 -
zone valve
thanks for the advice i appreciate it0
- 117 Geothermal