hydronic airhandler
dmmechanical
Member Posts: 3
help! I have a customer with a gas water heater that supplies a hydronic air handler. the system has been in for years. I went there on a service call tonight because there was cold air blowing from the diffusers. supply pipe was hot, but return was coming back cold. I tried purging the loop, I replaced the zone valve, and the circulator pump. The return will come back hot if I disconnect the fan and just let the pump circulate. As soon as the fan comes on, the return pipe goes cold. Any suggestions would be appreciated! Thanks!
Water Heater
What type of water heater do they have and where are the hydronic lines connected to it?Bob Boan
hydronic airhandler
it is a gas fired 40 gallon water heater and the hydronic lines are just piped in with tees off the domestic lines0 -
DIP Tube
Probably a failed dip tube in the tank water heater. When the fan is off the water just circs through, but with fan on and tube failed cooler water returns to tank and right back out the hot. This continuous cycle with water short circulating on the top of tank will do this.
The return line should have been teed into bottom drain connection
Does the tank do the domestic also? Dangerous but oh so often done. If so the DHW would go cold fast also I'm sure.
Just a guess though but seen it happen.
Very inefficient system though0 -
water heater
The water heater does do the DHW also. I will check tomorrow to see if the DHW runs out quickly. Thanks for the advice.0
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 107 Geothermal
- 983 Plumbing
- 389 Solar
