how to size Heating Boiler with no Btu info on tag. 1960 national boiler
mempho
Member Posts: 4
The tag says :
national boiler
sq'steam 1976000
sq'water 10550
sn# 4563
btu:
the info on the btu looks like it was never stamped. this is an atmospheric hot water boiler with two watts 3/4 174a 30 psi relief valves. it has a couple of end suction pumps that pump through it. I am struggling to figure out the size of this unit. it has a couple of 8"-10" stacks on it. nat gas burners on the bottom. this is the heat for an old Catholic school. anyone have any info on this boiler model number? or how to size based on the sq' of water? any help would be appreciated
national boiler
sq'steam 1976000
sq'water 10550
sn# 4563
btu:
Boiler Size
If the boiler is rated at 180 degrees, the output is 170 BTU's per square foot. So:
10,550 square feet x 170 BTU/square foot = 1,793,500 BTU
Deduct 15% for your I=B=R rating.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
The size
19W55 I believe the 55 may be horsepower so 33,479 BTU's per hr times 55 + 1,841,345 BTU's0 -
Please tell me
you are not sizing the new boiler off the old rating plate. I looked in my National book but your boiler is newer than my book.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0
- 85.7K THE MAIN WALL
- 50 Biomass
- 74 Chimneys & Flues
- 92 Geothermal
- 150 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 853 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.6K Strictly Steam
- 50 Water Quality
- 39 Industry Classes
- 15 Recall Announcements