Triagel Tube Solo Boiler Problem
 
            
                
                    JohnGL                
                
                    Member Posts: 1                
            
                        
            
                    Hi everyone, 
I have a solo 110 boiler that is supplying hot water to a restaurant.
I was called out last night because of no hot water.
I found the water pressure safety switch was leaking water.
Fortunately I had a replacement with me and replaced the switch.
Upon restoring power to the boiler the display shows "U 1.25".
I removed the cover on the Honeywell MCBA control and found a blown fuse just below the transformer terminals on the control.
I dried off the terminals to the pressure switch and checked other wiring.
Other than the foam lining the boiler being wet, everything seemed OK.
I replaced the fuse and restored power only to blow replacement fuse.
I then replaced the control board and the same fuse on the replacement control also blew.
I then removed the wiring harness cable from the control, replaced the blown fuse, restored power, blew fuse.
I switched transformers, replaced fuse, blew another fuse.
I rechecked wiring, everything seems to be OK.
I went to Radio Shack to get more fuses, 4 amp 250 V ?, all Radio Shack had was slow blow fuses.
Restaurant owner unhappy, I am not sure what to do next.
Any help would be appreciated!
Thanks.
                I have a solo 110 boiler that is supplying hot water to a restaurant.
I was called out last night because of no hot water.
I found the water pressure safety switch was leaking water.
Fortunately I had a replacement with me and replaced the switch.
Upon restoring power to the boiler the display shows "U 1.25".
I removed the cover on the Honeywell MCBA control and found a blown fuse just below the transformer terminals on the control.
I dried off the terminals to the pressure switch and checked other wiring.
Other than the foam lining the boiler being wet, everything seemed OK.
I replaced the fuse and restored power only to blow replacement fuse.
I then replaced the control board and the same fuse on the replacement control also blew.
I then removed the wiring harness cable from the control, replaced the blown fuse, restored power, blew fuse.
I switched transformers, replaced fuse, blew another fuse.
I rechecked wiring, everything seems to be OK.
I went to Radio Shack to get more fuses, 4 amp 250 V ?, all Radio Shack had was slow blow fuses.
Restaurant owner unhappy, I am not sure what to do next.
Any help would be appreciated!
Thanks.
0                
            Comments
- 
            TT F3 fuses
 If I understand you correctly that fuse is for the 24V side, did you check to see if there is a backfeed from another 24V source? Are you using the standard Smart tank aquastat?
 BTW-That Is a 4 amp 250V slow-blow fuse from factory.0
- 
            Find the problem?
 Just wondering if you found the problem?0
- 
            John try contacting
 Guy Wollard from TT e-mail gwooljr@comcast.net .0
- 
            One word
 Multimeter.
 You've got a short to ground or neutral. Likely from being wet. Ohm it out.0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements