Triagel Tube Solo Boiler Problem
JohnGL
JohnGL Member Posts: 1
Hi everyone,
I have a solo 110 boiler that is supplying hot water to a restaurant.
I was called out last night because of no hot water.
I found the water pressure safety switch was leaking water.
Fortunately I had a replacement with me and replaced the switch.
Upon restoring power to the boiler the display shows "U 1.25".
I removed the cover on the Honeywell MCBA control and found a blown fuse just below the transformer terminals on the control.
I dried off the terminals to the pressure switch and checked other wiring.
Other than the foam lining the boiler being wet, everything seemed OK.
I replaced the fuse and restored power only to blow replacement fuse.
I then replaced the control board and the same fuse on the replacement control also blew.
I then removed the wiring harness cable from the control, replaced the blown fuse, restored power, blew fuse.
I switched transformers, replaced fuse, blew another fuse.
I rechecked wiring, everything seems to be OK.
I went to Radio Shack to get more fuses, 4 amp 250 V ?, all Radio Shack had was slow blow fuses.
Restaurant owner unhappy, I am not sure what to do next.
 Any help would be appreciated!
Thanks.
  • TT F3 fuses
    If I understand you correctly that fuse is for the 24V side, did you check to see if there is a backfeed from another 24V source? Are you using the standard Smart tank aquastat?
    BTW-That Is a 4 amp 250V slow-blow fuse from factory.
  • Slimpickins
    Slimpickins Member Posts: 360
    Find the problem?
    Just wondering if you found the problem?
  • Tim McElwain
    Tim McElwain Member Posts: 4,660
    John try contacting
    Guy Wollard from TT e-mail gwooljr@comcast.net .
  • Tony_23
    Tony_23 Member Posts: 1,033
    One word
    Multimeter.
    You've got a short to ground or neutral. Likely from being wet. Ohm it out.