vaporstats
Steve_210
Member Posts: 647
installed my last mercury vaporstat today, I had obtained a few over the last few years. Have gotten alot of bad reports on non mercury type. Any advise, I don,t want to use just pressuretrols.
from what I have heard...
the new vaporstats are reliable enough, just not always properly calibrated. They do, however, have a provision for adjustment of the calibration. To do it, though, the system they are working on has to have a reliable low pressure gauge, preferably on the same pigtail.
But once they are calibrated they seem OK. And they don't have to be perfectly level...Br. Jamie, osb
Calibration ...
Am I right in concluding that the calibration is not as important as how the v-stat controls the operation of the boiler? By that I mean, assume you have a low pressure guage to meausure the pressure, you can could accept a miscalibration if you can find a setting that gives you the cut in and cut out that you want even if it does not precisely correspond to the cut in and cut out setting on the v-stat.0 -
thanks
thanks for the advise. I can;t see the proublem with a seperate pigtail. I always read oniy the 3lb guage when adjusting pressure0 -
FJL is right --
as long as the calibration isn't too far off, it really doesn't make a difference. I'm just one of those fussy types who likes to have their gadgets, if they have scales which read measurements, be at least reasonably correct... I also straighten things on shelves!Br. Jamie, osb
- 109 Chimneys & Flues
- 975 Plumbing
- 386 Solar
- 17 Recall Announcements
