Zone valves better on return?
JimX
JimX Member Posts: 12
Are zone valves better on the return than on the supply?
  • JStar
    JStar Member Posts: 2,752
    I've found.
    No significant difference on any jobs I've done, although I like to keep zone valves on the suction side of the pump to reduce noise on closing. And if you pump on the supply, they'll always be on the return.
  • JimX
    suction side
    Thank you, I think I will put my new setup that way.
    Jim
  • heatboy
    heatboy Member Posts: 1,468
    I prefer the supply side.....
    ...... if for no other reason than to assure there is no migration flow in the "off" zones.  If I were to put them on the return side, I would either use thermal traps or checks on each supply.