two pressuretrols vs vaporstats
SRC
Member Posts: 8
I currently have two pressuretrols wired for my boiler. I assume one is primary, the second is a backup. If I switched a pressuretrol to vaporstat can I leave the backup as a pressuretrol or do they both have to be the same? Two vaporstats are pricey.
you can switch only 1
if it's the case that you have an operation controller p-trol and a backup (manual reset) p-trol .. you only have to switch the operation control...1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Will work fine
Second that. When I discovered that my system was a vapor system, I replaced one of two pressuretrols with vaporstat. Has worked like a champ for 10 yrs.
set your cut in and cutout on the pressuretrol a little wider than on your vaporstat; that way the vaporstat runs the show and, in the event of vaporstat failure, your pressuretrol keeps things in check.
Best of luck,
Eli0 -
Is your system a
powerpile self generating system?0