Steam Boiler replacement BTU question

JohnsBoard
Member Posts: 2
<a href="file:///C:/DOCUME~1/John/LOCALS~1/Temp/msoclip1/01/clip_filelist.xml">
[url=file:///C:/DOCUME~1/John/LOCALS~1/Temp/msoclip1/01/clip_filelist.xml]
I am changing my steam
boiler from oil to gas. I currently have a HB Smith boiler with a Beckett
blower with a .85 nozzle. I looked at the Weil McLain instructions on there
website and calculated my radiators to be only 46,905.04 BTU’s. I also have a
hot water loop in the basement with a ten-foot baseboard. The plumbers I know
tell me I should use a 100,000 BTU boiler. Is that too much? I just want it to be efficient as possible.
The system I use now seems to use a lot of oil for a small house, total 1066 square
feet for the first and second floor. My roofline is steep so the second floor
has a lot of un insulated roof on the walls but the attic floor is insulated.</a>
[url=file:///C:/DOCUME~1/John/LOCALS~1/Temp/msoclip1/01/clip_filelist.xml]
I am changing my steam
boiler from oil to gas. I currently have a HB Smith boiler with a Beckett
blower with a .85 nozzle. I looked at the Weil McLain instructions on there
website and calculated my radiators to be only 46,905.04 BTU’s. I also have a
hot water loop in the basement with a ten-foot baseboard. The plumbers I know
tell me I should use a 100,000 BTU boiler. Is that too much? I just want it to be efficient as possible.
The system I use now seems to use a lot of oil for a small house, total 1066 square
feet for the first and second floor. My roofline is steep so the second floor
has a lot of un insulated roof on the walls but the attic floor is insulated.</a>
0
Comments
-
Boiler sizing
There is no good reason to install a boiler that is more than twice the size needed to fill radiators with steam.
It leads to inefficiency and imbalance.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting
Plumbing in NYC or in NJ.
Take his class.0 -
Agreed
if it's using a lot of oil, the boiler may or may not be the problem. Have you had a Steam Man look at your system?
Try the Find a Professional page of this site.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Based on your
BTU on the radiators a boiler around 75,000 is more than enough and if you get a Mod/Con boiler with outdoor reset you will be able to dial it in for real good efficiency and comfort. I would also however have a heat loss done on the house to be able to match that up with the radiation. I might also suggest TRv's on the radiators with constant circulation.0 -
Whoops I should go to bed
I am tired I didn't realize your boiler was a steam boiler, sorry. Still I would have a heat loss done and as Steamhead suggested you may have issues with the system itself.0
This discussion has been closed.
Categories
- 120.9K All Categories
- 83.9K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 415 Carbon Monoxide Awareness
- 34 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 117 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 49 Pipe Deterioration
- 745 Plumbing
- 5.3K Radiant Heating
- 358 Solar
- 13.9K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 37 Industry Classes
- 71 Job Opportunities
- 14 Recall Announcements