Steam Boiler replacement BTU question
JohnsBoard
Member Posts: 2
<a href="file:///C:/DOCUME~1/John/LOCALS~1/Temp/msoclip1/01/clip_filelist.xml">
[url=file:///C:/DOCUME~1/John/LOCALS~1/Temp/msoclip1/01/clip_filelist.xml]
I am changing my steam
boiler from oil to gas. I currently have a HB Smith boiler with a Beckett
blower with a .85 nozzle. I looked at the Weil McLain instructions on there
website and calculated my radiators to be only 46,905.04 BTU’s. I also have a
hot water loop in the basement with a ten-foot baseboard. The plumbers I know
tell me I should use a 100,000 BTU boiler. Is that too much? I just want it to be efficient as possible.
The system I use now seems to use a lot of oil for a small house, total 1066 square
feet for the first and second floor. My roofline is steep so the second floor
has a lot of un insulated roof on the walls but the attic floor is insulated.</a>
[url=file:///C:/DOCUME~1/John/LOCALS~1/Temp/msoclip1/01/clip_filelist.xml]
I am changing my steam
boiler from oil to gas. I currently have a HB Smith boiler with a Beckett
blower with a .85 nozzle. I looked at the Weil McLain instructions on there
website and calculated my radiators to be only 46,905.04 BTU’s. I also have a
hot water loop in the basement with a ten-foot baseboard. The plumbers I know
tell me I should use a 100,000 BTU boiler. Is that too much? I just want it to be efficient as possible.
The system I use now seems to use a lot of oil for a small house, total 1066 square
feet for the first and second floor. My roofline is steep so the second floor
has a lot of un insulated roof on the walls but the attic floor is insulated.</a>
0
Comments
-
Boiler sizing
There is no good reason to install a boiler that is more than twice the size needed to fill radiators with steam.
It leads to inefficiency and imbalance.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Agreed
if it's using a lot of oil, the boiler may or may not be the problem. Have you had a Steam Man look at your system?
Try the Find a Professional page of this site.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Based on your
BTU on the radiators a boiler around 75,000 is more than enough and if you get a Mod/Con boiler with outdoor reset you will be able to dial it in for real good efficiency and comfort. I would also however have a heat loss done on the house to be able to match that up with the radiation. I might also suggest TRv's on the radiators with constant circulation.0 -
Whoops I should go to bed
I am tired I didn't realize your boiler was a steam boiler, sorry. Still I would have a heat loss done and as Steamhead suggested you may have issues with the system itself.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements