W-M Ultra owners/installers, take note
If there is corrision on the out side, there will be corrision on the inside as well. I would take heat exchanger apart to clean boiler(should be done annualy) to be sure condensate is running through boiler properly!
  • Xc8p2dC
    Xc8p2dC Posts: 41
    Corrosion
    I recently had an Ultra80/S2 go into lockout with a E29 error code [Blower/fan not at zero]
    Upon inspection, the blower is directly under the air intake port, and suffered abnormal corrosion after 3 years
    I live on the coast, less than a mile from the ocean and build up seems to be related to salty air/fog/rain
    So far, cleaning the ground strap, has not let problem return as of yet
    I wonder if the series 3 is designed the same way?
  • Tony_23
    Tony_23 Posts: 1,033
    other cause
    Same thing can happen with cross-contamination by flue gas. A larger separation between intake and exhaust usually cures it.
  • That Location
    is less than ideal in very cold climates too. I have had them freeze solid from ingesting ice cold air through the vent holes in the top of the air horn. W/M suggested solution was to install a deflector shield to divert ice cold air away from the motor. Of course there is lots of room for that!!
    Quality design!?!?
  • Xc8p2dC
    Xc8p2dC Posts: 41
    Nope
    Not the ground, error code/lockout came back, I noticed this time that 2 007 circs continute to run as well.
    Reset and disconnect allow it to fire back up once blower stopped
    Currently got it running at LF, so it will not cycle off, gong to be single digits this weekend
    Anyone else experiance this lockout? /fix
  • E29 onUtra 155
    I had the same problem this month. It is about 3 years old. How can i run at LF? what does the LF mean?
    I talked to a technican at W-M. He said the blower motor is bad. It seems that the whole blower assembly kit needs to be replaced, although the blower can run. Do I really need to replace the whole assembly kit?
    By the way, how can I open the blower?
    Thanks.
  • Xc8p2dC
    Xc8p2dC Posts: 41
    Not to worry
    Should be coverered under factory warranty if you registered your boiler with WM
    Their not simple fans anymore, not servicable, lots of electronics in it and plays a big part of system operations>> LF is low fire, worked in my situation, but not everyones
  • tommyoil
    tommyoil Posts: 612
    Hey Tony
    You sure you know what you're talking about??? Did you take the "pro" test yet? Just wondering.
  • Tony_23
    Yeah, TO
    I finally did pass, after I installed a new system in my own house. The couple thousand before that don't count ;)
    Inducers, blowers, pressure switches, all the same and all have 'em right ?
    Ooohhh, my sarcasm isn't "nice", I should stop.....
  • tommyoil
    tommyoil Posts: 612
    I knew you could do it
    Cheerios are on me next time.
  • Thanks
    I will contact W-M. It seems that the W-M really has quality problem. My system has broken twice this year after it passed 3 years.
  • Would you tell me how to set up at LF status?
    I would like to know how to set up at the low fire status. I need to try to start the boiler up now before it is fixed. Thanks.
  • Tony_23
    LF
    If it doesn't fire up when you reset it, it doesn't matter.